Scan Device on different subnet BMCNOC0321

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Re: Scan Device on different subnet BMCNOC0321
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
11
YONGHO-KIM
Lieutenant YONGHO-KIM Lieutenant
9
ciupol
Lt. Commander ciupol
9
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Start a Topic
eldod16
eldod16
Cadet

Posted: ‎2024-11-23 11:21 AM

0 Likes
4
1035
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-23 11:21 AM

Scan Device on different subnet BMCNOC0321

Hi, 

I need to scan a device (DTM) on a BMENOC0321, but the device is on a diffrent subnet than the NOC card itself. 

How can this be acoomplished?

*Note: There is a router on the network and the traffic can pass. 

*Note: This can be accomplished using a BMENOC0301 card, but my application limit my options.

 

Running BMEP584040 Control Expert 14.1

Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • 06. EcoStruxure Control Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Siddiqui
Ensign Siddiqui Ensign
Ensign

Posted: ‎2024-11-26 08:05 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-26 08:05 AM

Hi @eldod16,

 

Please share the network architecture along with the IP address schemes and how the different nodes are connected. It becomes easy to understand and answer to your request.

 

BMENOC0321 came with the IP forwarding feature, and this module can support up to three subnets.

 

I don't know how this module is configured inside the ECE (Control Expert) in your configuration.

When you said that this could be accomplished with the BMENOC0301 card, could you please explain this, or when you are trying to configure device scanning in a different subnet using BMENOC0321, you are facing an error inside the ECE? If that is the case, please share the error message.

 

NOTE: The control ports, which are Port 2 and Port 3 of the BMENOC0321 module, are the ones able to scan the devices either using Modbus TCP or Ethernet IP.

 

I did some configuration in my setup, but I am using ECE V 16.0.

 

In my configuration, I am not using the IP forwarding feature inside the NOC0321 module to make it simple.

 

For example, the control ports (Port 2 and Port 3) of the NOC0321 module are in Network A. Check the snapshot for your reference:

 

IP Address: 172.168.12.1

Subnet Mask: 255.255.255.0

Gateway: 172.168.12.10 (This is the Router IP address where the BMENOC0321 is connected with the Router port)

Siddiqui_0-1732636797725.png

 

After opening the DTM configuration of the BMENOC0321 module, I added the Generic Modbus TCP inside the DTM and did the following configuration:

IP Address: 192.168.12.3

Subnet Mask: 255.255.255.0 (Grey out)

Gateway: 172.168.12.1 (Grey out)

NOTE: DHCP is disabled by default for this generic Modbus TCP device. I enabled the DHCP option, corrected the GATEWAY IP Address, and deactivated it again.

Siddiqui_1-1732636797727.png

 

 

The Ethernet Network Manager summarises the BMENOC0321 control port Network and the Modbus TCP device network address.

Siddiqui_2-1732636797730.png

 

 

I managed to build the ECE project with just a warning:

Siddiqui_3-1732636797731.png

 

I believe this should work as the BMENOC0321 module should pass scanning Modbus TCP device information to the gateway address, and for the rest, the router does the job. You have to make sure that the proper gateway configuration is done on the other side of the router where the device is connected.

 

NOTE: I never tested such configuration by myself. Theory-wise, it looks good, but I recommend you do the test to make sure it works. If you are facing issues, please collect the Wireshark logs and share them with me. Even if you plan to enable the IP forwarding feature inside the BMENOC0321, the device scanning should be the same as explained above.

 

I hope the above comments will provide help.

 

BR,

MWS

 

Reply

Link copied. Please paste this link to share this article on your social media post.

eldod16
eldod16
Cadet

Posted: ‎2024-11-26 09:16 AM

1 Like
1
955
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-26 09:16 AM

Hi @Siddiqui 

 

Thank you for your nice detailed answer. 

 

The method you have described is what I normally use when doing such scanning on different subnets from a BMENOC0301. 
The issue i am facing is that when doing this on a BMENOC0321, ECE won't allow me to save the IP setting for the DTM. For the sake of testing, i repeated the exact same steps as you on a new project. The NOC0321 is not configured for IP forwarding.

eldod16_0-1732640074795.png

eldod16_1-1732640122296.png

 

 

eldod16_3-1732641247162.png

eldod16_4-1732641322129.png

eldod16_5-1732641337747.png

 

I am starting to think this might be a limitation of ECE v14.1, I will try to install and test this on V15.3

 

Thank you

 

 

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Siddiqui
Ensign Siddiqui Ensign
Ensign

Posted: ‎2024-11-27 06:11 AM

In response to eldod16
0 Likes
0
931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-27 06:11 AM

Hi @eldod16,

 

Yes, I agree with you. This limitation seems to come from an older version of ECE 14.1.

Using ECE V15.3, after adding the BMENOC0321 module, followed by adding the device using DTM and then trying to change the IP address of the device into a different subnet, which is not possible in the ECE V15.3.

 

Check the snapshot for your reference:

Siddiqui_0-1732716317696.png

 

We also repeat the same steps using ECE V15.3 with BMENOC0301/0311, which allows the scan of devices from different subnets but not for the BMENOC0321.

 

In my earlier post, I shared that ECE V 16.0 allows the scan of devices from different subnets for BMENOC0321. It seems that from ECE V16.0 and onwards, all the modules BMENOC/0301/311/0321 support this feature.

 

NOTE: I suggest you perform the test with ECE V16.0. I was looking at whether there might be any HF for ECE V15.3 that might allow the BMENOC0321 module to scan the device from a different subnet, but I was not able to find it. You can also try it.

 

I hope the above comment provides help.

 

Best Regards,

MWS

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Trinxs1
Lt. Commander Trinxs1 Lt. Commander
Lt. Commander

Posted: ‎2024-11-28 05:45 PM . Last Modified: ‎2024-11-28 05:48 PM

0 Likes
0
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-28 05:45 PM . Last Modified: ‎2024-11-28 05:48 PM

V15.3 supports allocation of a EIP and Modbus TCP device to a BMENOC0301/311 which is in a different subnet.  Expert V16 supports this for a CPU as well.  I have tried adding devices to a BMENOC0321 in V16.0 and confirm the project builds when I use EIP and MBT devices located in a different subnet to the BMENOC0321 module.
You will need to make the EIP communications point to point and not multi-cast. It is unusual that once the change was made, I had to enable the address server and then disable it to refresh the configuration screen.  The gateway IP address has to be in the same remote subnet for the EIP changes to be accepted, however with the MBT there was not option to change.  Attached is a screen shot of my configuration which has EIP devices connected to ethernet modules including the CPU with IP addresses in a different subnet.

Trinxs1_0-1732844717186.png

 

Trinxs
Senior Technical Sales Consultant - PAC
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore