Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
Back to Modicon PAC Forum
SIGE_BMR
SIGE_BMR
Explorer
Posted: โ€Ž2025-09-12 03:02 AM
2737
I'm trying to read the values on a flow meter via Modbus TCP with a M340 CPU and a NOE card.
The hardware configuration goes like this: Flow meter -> Modbus RTU to TCP Gateway -> NOE.
When I use a Modbus TCP Client on my PC (simply Modbus), I can read the modbus register just fine.
I use the function 4 "Read Input Registers", and I'm reading for example the 30103 register.
To do this in Control Expert (License XL and V16.0 by the way), I wrote this code in the MAST task:
GEST_READVAR[2] := 50;
IF NOT GEST_READVAR[0].0 THEN
READ_VAR (ADR := ADDM('Ethernet_1{192.168.50.153}1'), OBJ := '%IW', NUM := 30103, NB := length_arint(RECP_READVAR), GEST := GEST_READVAR, RECP => RECP_READVAR);
END_IF;
reTest := WORD_AS_REAL(LOW := INT_TO_WORD(RECP_READVAR[0]), HIGH := INT_TO_WORD(RECP_READVAR[1]));
(RECP_READVAR is an ARRAY[0..1] OF INT, reTest is a REAL).
Currently, the values of lines 0 and 1 in the RECP array are both 0, but simply modbus displays other values, so something must be wrong but I don't know what.
Does anyone have an idea of what I can do to make this work?
(you can find the datasheet of the Modbus RTU module attached to the topic, with register numbers on pages 19 to 26)
Thanks a lot for the time anyone would take to look into this๐Ÿ˜€
  • 01. Modicon M340 PAC
  • 05. Networking & Communication
  • 06. EcoStruxure Control Expert
ProfHameedi
ProfHameedi Troubleshooter
Troubleshooter
Posted: โ€Ž2025-09-14 07:55 AM
2
2711
Hello @SIGE_BMR
As per the above issue's description, I can guess almost sure that the issue is related to the NUM value which refers to the starting register index.
The correct value is NUM=102 which means Modbus 103 as M340/M580 are based on IEC0 but your device is based on IEC1, and the suffix 3 means the data type is Input Register which has already included in the OBJ="%IW".
You may try this and feedback me.
Replies 4
ProfHameedi
Troubleshooter
2
2712
Hello @SIGE_BMR
YONGHO-KIM
YONGHO-KIM Mentor
Mentor
Posted: โ€Ž2025-09-14 06:02 PM
"Modbus address 30103 actually corresponds to address 103 (0-based), so you should set NUM := 103."
SIGE_BMR
SIGE_BMR
Explorer
Posted: โ€Ž2025-09-14 11:37 PM
In response to ProfHameedi
1
2662
Hello @ProfHameedi
I tried your suggestion of using 102 for the NUM parameter and it worked!
I also had other Modbus registers to read on the device, all within the 30XXX range, and everything worked by sustracting 30001 to the register value and using the result as the NUM parameter.
Thank you so much for your help ๐Ÿ™
Have a great day ๐Ÿค™
ProfHameedi
Troubleshooter
Posted: โ€Ž2025-09-15 03:51 AM
In response to SIGE_BMR
Thanks for your feedback.. It is nice to hear that.
ย
WHATโ€™S NEXT?
Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2026 Schneider Electric