Posted: 2024-06-20 05:34 AM
I have a bunch of remote IO communicating over Ethernet/IP thru a BMXNOC401.2 card. Does anyone know if that I/O is scanned such that its synchronous or asynchronous to the PLC logic?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-23 09:19 PM
I would think that almost all comms are asynchronous. I mainly say this because the READ_VAR FB explicitly states that it requires multiple scan cycles for execution. Even the default repetitive rate of the IO scanner is in the hundreds of millisecond range.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-25 07:16 AM
I might be doing something wrong. I did not think its necessary to use a READ_VAR_FB. The I/O is coming into a BMXNOC401.2 card and the devices are Itoh Denki IB-E03 cards. When I added them to the device list for the 401 card it assigned memory addresses and shows a Scan Rate of 30ms.
I have a meeting with Schneider Electric Tech support this coming Thursday. I'll run my configuration by them.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-26 05:06 AM
You're correct that you don't need to use the READ_VAR blcoks, since you are using the IO scanner built into the BMXNOC401.
Pleas share the response for tech supoport when you can, I'd also like a difinitive answer to where or not the IO scanning is synchronous or asynchronous.