Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Multiple Issue in Configuring Advantys STBNIP2212 Ethernet TCPIP MB TCP/IP module...

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Multiple Issue in Configuring Advantys STBNIP2212 Ethernet TCPIP MB TCP/IP module...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
Modicon STB (Advantys)

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Start a Topic
Solved
hemant2309
hemant2309
Explorer

Posted: ‎2024-01-25 05:50 AM

0 Likes
6
5636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-25 05:50 AM

Multiple Issue in Configuring Advantys STBNIP2212 Ethernet TCPIP MB TCP/IP module...

Hii,

I am facing the multiple issue in configuring the Advantys Advantys STBNIP2212 Ethernet TCPIP MB TCP/IP  modules, I am not sure is it software issue or product

 

I have already configure islands where STBNIP2212-V2.x with IO modules were used, the new NIM module i received is V4.0 and V3.0 hence in current backup change the NIM modules to STBNIP2212-V4.x and then try connect with standard procedure ......

  >> configuration mismatch messege popups and imedietly it asks confirmation to upload from NIM and overwrites the existing configured island and gives some "9: Subscript out of range" messege continously.. no download into island option window apear. 

>> If create a blank island and try to connect with NIM using default IP from MACID, suddenly application crashes..

 

I have tried this with Advantys software V7.0, V12.0 and V12.3 everywhere facing the same issue.

 

Kindly help to findout the issue, some sample error messege enclosed for referance.

Attachments
Labels
  • Labels:
  • 04. Modicon X80 IO
  • 05. Networking & Communication
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MatthewM
MatthewM
Mentor

Posted: ‎2024-02-04 04:57 PM . Last Modified: ‎2024-02-04 05:00 PM

In response to hemant2309
0 Likes
1
5585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-04 04:57 PM . Last Modified: ‎2024-02-04 05:00 PM

As far as I know, the STBNIP2212 FW only goes to 4 so far.  The STBNIP2311 is version 5.  It is possible that tech support have confused the two models.  2212 is older 1 port device.  2311 is newer dual port device.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Trinxs1
Trinxs1 Leader
Leader

Posted: ‎2024-01-29 09:13 PM

0 Likes
3
5630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-29 09:13 PM

Have you raised this issue with technical support?

Trinxs
Senior Technical Sales Consultant - PAC
Reply

Link copied. Please paste this link to share this article on your social media post.

hemant2309
hemant2309
Explorer

Posted: ‎2024-02-01 08:08 PM

In response to Trinxs1
0 Likes
2
5597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-01 08:08 PM

Yes raised to Technical Support, they have advised to update the firmware of STBNIP to 5.X with advantys configurator V12.3.

However i couldnt able to locate the STBNIP firmware file V5.X on schneider website hence request to provide the same.

Warm regards

Hemant

Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
MatthewM
Mentor

Posted: ‎2024-02-04 04:57 PM . Last Modified: ‎2024-02-04 05:00 PM

In response to hemant2309
0 Likes
1
5585
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-04 04:57 PM . Last Modified: ‎2024-02-04 05:00 PM

As far as I know, the STBNIP2212 FW only goes to 4 so far.  The STBNIP2311 is version 5.  It is possible that tech support have confused the two models.  2212 is older 1 port device.  2311 is newer dual port device.

Reply

Link copied. Please paste this link to share this article on your social media post.

hemant2309
hemant2309
Explorer

Posted: ‎2024-02-13 11:26 PM

In response to MatthewM
0 Likes
0
5524
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-13 11:26 PM

Yes...Schneider Support team later clarified latest Firmware is 4 only, and they provide the same file.. 

Reply

Link copied. Please paste this link to share this article on your social media post.

hemant2309
hemant2309
Explorer

Posted: ‎2024-02-14 12:37 AM

0 Likes
1
5521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-14 12:37 AM

After upgrading firmware also i was facing the same issue.

 

Initially we just powered on NIP2212 in my office, no PDT and other Signal modules and end plates connected like in my offline configuraion, and we were trying to download, where we were facing the issues. 

 

Later  We physically add one PDT module and one Signal module to the NIM, and try to download the island configurations, everything works fine, we can easily download the configuration and go online with NIM..

 

I checked the documents however not able to find the information/Instructions that NIM Module in standalone can not accept the configuration like the way we were trying.

 

Anyways My issues is resolved, thank you for replies..Rack.PNG

Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
MatthewM
Mentor

Posted: ‎2024-02-15 10:53 AM

In response to hemant2309
1 Like
0
5511
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-15 10:53 AM

Well done.  I think it would require at least the endplate.  I have not tried with only the NIP and no other cards that I recall, but it definitely doesn't like a missing endplate.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.