Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Modicon Quantum Remote I/O Rack Problem (IOs Communication or Drop-out)

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Modicon Quantum Remote I/O Rack Problem (IOs Communication or Drop-out)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
Modicon Quantum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2022-09-24 10:17 AM . Last Modified: ‎2022-09-24 12:46 PM

2 Likes
0
3501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-24 10:17 AM . Last Modified: ‎2022-09-24 12:46 PM

Modicon Quantum Remote I/O Rack Problem (IOs Communication or Drop-out)

System Details:

We use hot redundant Modicon Quantum PLC  with dual redundant communication having Remote IO racks (using CRP + CRA cards and coaxial cable). One rack is for Hot Redundant CPUs and other 12 racks are for Remote IO Drops (total 13 Drops). The model numbers of installed cards are given below

 

  1. CPU: 140 CPU 434 12A (486 Controller)
  2. RIO Head: 140 CRP 932 00
  3. RIO Drop: 140 CRA 932 00
  4. Software: ProWORX  32
  5. Dual redundant communication using Coaxial Cable and splitters

 

Problem Faced and Action Performed:

 

A. Our plant was running and tripped without any process abnormality. Most of inputs configured in different DI cards of the rack 2 actuated at the same time, which triggered the tripping. The same was diagnosed from the alarms history on HMI. No evidence of system / rack failure was found on CPU/CRA/CRP or HMI.

 

We replaced the CRA (RIO Drop) card of the rack 2, as this could be the single point of failure.

 

B. The plant was started again, but some hours later, the same nature of problem and alarm from inputs of DI cards were observed.

 

This time the Drop's back-plane and DI cards of actuated inputs were replaced.

 

C. The plant was started again and to our surprise, tripping happened again after a few hours with same alarms .

Upon further troubleshooting, PLC Status tab of ProWORX 32  an  Overrun error in word #175 and word #178 were found.  

 

Based on the errors, PV and SV versions of CRA cards of all racks were compared. Their SV versions were in the range of 1.XX. whereas the only 1 CRA card  had the SV of 2.00, which was replaced initially during Action  mention in para A. 

 

Therefore, the card with SV2.00 in drop 2 was replaced with SV version 1.26.

 

D. After this activity the plant was started again and is running in normal state till the time of writing 😊.

 

Questions:

 

  1. What could be the possible causes of these nuisance trippings?
  2. Can the difference in PV and SV versions of CRA/CRP  card, result in such trippings ? If yes, Is there any compatibility matrix.
  3. What is probable cause of Overrun Error ? Is there any relation of this error with these trippings?
  4. Do you have any case study and example of such nature of trippings? 
  • Tags:
  • CRA Firmware versions
  • Overrun error
  • SV and PV versions
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 0
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore