Modicon PAC Forum
A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-08-17 12:47 AM
There are those in which the ERR LED of the module is flashing and the ones in which the ERR & IO LED is flashing.
I would like to know the cause of this phenomenon and how to fix it.
Attached is a video of the phenomenon.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-22 01:44 PM
The LED light pattern is described on pp57 of this manual:
https://www.se.com/ww/en/download/document/35011978K01000/?searchSource=guided
Is the module correctly configured in Control Expert?
Have you tried re-seating the module (remove and replace)?
What diagnostics or data can you read via Control Expert online?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-09-22 08:42 PM
Hi @Parksunguk !
IO LED- Constant: Means one of the 8 channels of AMI0810 Card is spare and not connected to any physical input.
IO & ERR LED- flashing: 1. Any of your AI signal is having opposite polarity i.e. wring connection to the card.
2. It might be possible that you might configured your card for 1-10V but your AI signal is of 4-20mA range or vice versa.
In case of LED Flashing sometimes after troubleshooting, it requires to give a power restart to the particular rack.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.