Modicon M340 OPC UA UMAS_Protocol Error
Modicon PAC Forum
Select a Country
  • Industrial Automation
  • Modicon PAC Forum
  • Modicon M340 OPC UA UMAS_Protocol Error
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
Modicon M340
Back to Modicon PAC Forum
Posted: ‎2022-06-08 07:37 AM
4
3925
Hi
I am trying to connect to a few Modicon M340 PLCs using OPC UA. I have followed the instructions in the video here: https://www.se.com/ww/en/faqs/FA411749/
I am successfully able to connect to 2 of my PLCs, but I am unable to connect to the rest.
I get the same error for all the other PLCs as is shown in the attached image.
The only difference I can see is that on the 2 PLCs that connect they have newer firmware than the rest.
Do I need to upgrade the firmware on the other PLCs to be able to connect using OPC UA?
Or is there another reason for why I am unable to connect to them?
I can't find anything about these error codes online
Thanks in Advance
Aron
  • m340
  • opc ua
Replies 4
Posted: ‎2022-06-30 11:58 PM
@Anonymous user wrote:
Hi
Thanks in Advance
Aron
Did you get any solution?
RoozeeR
RoozeeR Mentor
Mentor
Posted: ‎2022-07-01 12:36 AM
3794
1: Did you check in Unity/Control Expert if the checkbox " DataDictionary" is selected? See screenshot attached, DataDictionary enabled is mandatory.
2: And if yes, is the checkbox "Only HMI Variables" also selected? Then check if there are variables with in the Data Editor, which have the checkbox HMI variables selected.
3: If the checkbox "Only HMI Variables" is not selected all variables should be exposed in the Data Dictionary to OPCUA when he checkbox " DataDictionary" is selected.
If all this is set, please check the firmware used in the CPU and NOC/NOE (if used) cards.
R.Roozee
Sr Solution Architect (SAE Master)
Posted: ‎2022-07-08 04:42 AM
In response to RoozeeR
3706
Hi
Thanks for the answer.
I have the "DataDictionary" checkbox selected and I have tried it with and without the "Only HMI Variables" checbox checked. In both cases I get the same error as mentioned in my original post.
The firmware I have on the CPUs that don't work is 2.10 and 2.00.
The firmware I have on the CPUs that work is 2.60
Thank you
Aron
RoozeeR
RoozeeR Mentor
Mentor
Posted: ‎2022-07-08 05:54 AM
In response to Anonymous user
Hello Aron,
There is your answer. V2.00 and v2.10 are rather old.
Best to upgrade the CPU's to latest version (3.40), which also bring a lot of improvements to Cyber Security issues.
Also you might consider to upgrade your application (CPU type version in Unity/ECE).
br
R.Roozee