Modbus Over TCP/IP, DATA_EXCH Not Working for Code 05h (Write To Coil)

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Modbus Over TCP/IP, DATA_EXCH Not Working for Code 05h (Write To Coil)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
11
YONGHO-KIM
Lieutenant YONGHO-KIM Lieutenant
9
ciupol
Lieutenant ciupol
9
RoozeeR
Lt. Commander RoozeeR Lt. Commander
8
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Start a Topic
ANF-Energy
Crewman ANF-Energy
Crewman

Posted: ‎2024-10-22 11:00 AM

0 Likes
2
768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 11:00 AM

Modbus Over TCP/IP, DATA_EXCH Not Working for Code 05h (Write To Coil)

I am still new to M580 and getting Modbus over TCP/IP working. I got read register (code 03h) to work but cannot get write to coil (code 05h) using function block DATA_EXCH to work. Here are my code samples along with the M580 manual references I am using and the protection relay I am writing to a 1 bit register ("coil"), if someone can pinpoint the error:

 

ANFEnergy_0-1729619706835.png

ANFEnergy_2-1729619787066.png

 

ANFEnergy_3-1729619808061.png

ANFEnergy_4-1729619865321.png

 

-----------------------------------------
Andrew Liam McNeil
Systems & Software Engineer
ANF Energy Solutions Inc.
Email: almcneil@anfenergy.ca
Website: www.anfenergy.ca
Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • 06. EcoStruxure Control Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
HAIBO
HAIBO Support
Support

Posted: ‎2024-12-24 05:11 PM

0 Likes
0
625
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-24 05:11 PM

You may try this demo DFB to send FC5 

Attachments
fc5.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2024-12-26 12:42 PM

0 Likes
0
604
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-12-26 12:42 PM

Please check your data types and data packing.  I think your issue is that you need to re-pack the data correctly.  The Tx_Data array is INT, but the manual shows the structure as BYTE, WORD, BYTE.  You might be better off working in a raw data BYTE array to build up the query, and then use BYTE_AS_WORD and WORD_TO_INT to push into the Tx_Data array for EMIS.

 

PS - do you need to use the DATA_EXCH?  I think you would only use this if you expect a response form the device following the command.  The standard Modbus WRITE_VAR can also write to coils, and READ_VAR can read all Modbus types.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore