Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

M580 hot standby initiate CPU swap-over when a primary rack Ethernet module has a fault

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • M580 hot standby initiate CPU swap-over when a primary rack Ethernet module has a fault
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
Modicon M580
product field
Schneider Electric
EcoStruxure™ Control Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Start a Topic
Trinxs1
Trinxs1 Leader
Leader

Posted: ‎2021-04-07 10:32 PM . Last Modified: ‎2021-04-07 10:49 PM

1 Like
1
4415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-07 10:32 PM . Last Modified: ‎2021-04-07 10:49 PM

M580 hot standby initiate CPU swap-over when a primary rack Ethernet module has a fault

Swapping a hot standby primary system on the failure of a primary CPU rack NOC module.

 

I wanted to share code we developed locally for swapping the hot standby system if a NOC module in the primary rack was faulty as long as the standby system is OK.

 

I have placed extensive comments in the logic.

It is based on system which has two NOC modules in each rack. One pair of NOC modules (primary and Standby) manage an RSTP ring of drives and the other NOC module pair manage an RSTP ring of motor protection units.

 

If we have a primary ethernet module fault as long as there is no fault in the standby CPU rack i.e. CPU or ethernet modules we will initiate a swap-over of the primary CPU.  Please note that any fault condition in the standby i.e. CPU has no connection to ERIO, a fault in the either NOC module, the CPU is not in run and in standby mode the logic will not swap over due to a NOC module fault.

 

The normal CPU swap over reasons i.e. failure of the primary CPU, primary CPU in stop, loss of comms to ERIO or loss of power to primary CPU will always trigger a swap-over to the standby.  The ethernet logic does not impede this.

 

Please also note I did not use the IO scanner status as the failure of one device can cause this to fault and with 20 or 30 devices we still wish to communicate with as many as possible.

 

Hopefully this is of value to others.

 

https://schneider-electric.box.com/v/M580HSBY-Swap-NOCFail - Please ask if you want a copy of the project files if not attached to this message.

Trinxs
Senior Technical Sales Consultant - PAC
Attachments
HSBY Failover on Ethernet failure.7z
Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • 06. EcoStruxure Control Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Robert_Willis
Robert_Willis Troubleshooter
Troubleshooter

Posted: ‎2021-04-08 07:28 AM

0 Likes
0
4398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-08 07:28 AM

Perfect timing !!! i have a customer that is migrating an existing Modicon Quantum HSBY with multiple 140NOE771x1 modules. They are currently using the 140NOE771xx detection and swapping logic.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore