M580 HSBY with Dual (redundant) OPCUA network

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • M580 HSBY with Dual (redundant) OPCUA network
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
MatthewM
Lt. Commander MatthewM
8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
7
Trinxs1
Lt. Commander Trinxs1 Lt. Commander
6
ciupol
Lieutenant ciupol
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2023-07-19 09:04 AM . Last Modified: ‎2023-07-19 09:07 AM

0 Likes
8
2327
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-19 09:04 AM . Last Modified: ‎2023-07-19 09:07 AM

M580 HSBY with Dual (redundant) OPCUA network

My customer wants to implement a M580 HotStandby with a dual OPCUA connection to a redundant SCADA server. Dual network for redundancy reason.

See attached network architecture of A M580 HSBY system with Dual BMENUA0100 server. According to the documentation 2 BMENUA0100 modules can be used in a M580 system (4 total in a HSBY).

The BMENOC modules are used for communication to different other systems in separated networks.

 

Question: Do you have any remarks, attention points, or good/bad experience using dual BMENUA0100 modules in a HSBY?

System Architecture OPCUA.png

R.Roozee
Sr Solution Architect (SAE Master)
Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • 05. Networking & Communication
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
KJBER
Ensign KJBER
Ensign

Posted: ‎2023-07-20 12:32 PM . Last Modified: ‎2023-07-20 12:34 PM

2 Likes
0
2237
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-20 12:32 PM . Last Modified: ‎2023-07-20 12:34 PM

I tried with one NUA card in each PLS rack, with Aveva as Scada system. We had to make custom scripts in scada to investigate the service level and isbadquality of the OPC UA connections from the NUA communication cards, and also force PLC changeover from SCADA with this setup. The NUA also seem to have a slow samling intervall (0.5-3 seconds) when you have many tags (2000+ tags).

 

Based on this one project then I would not recommend it. Use NUA cards if you have to share certain variables with 3 party vendor with a OPC UA server, and use conventional connection to scada.

 

Hopefully it will get better in the future.

Reply

Link copied. Please paste this link to share this article on your social media post.

Trinxs1
Lt. Commander Trinxs1 Lt. Commander
Lt. Commander

Posted: ‎2023-07-20 09:12 PM

0 Likes
1
2227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-20 09:12 PM

My comment does not relate specifically to Hot standby.
I have a customer who is using NUA modules in a hot standby system and sees the limit of 50000 tags per module as a concern.  I assume that by having two modules we can access 100000 nodes (tags) per CPU.

Does anyone else have customers who require access to more than 100 000 tags?

 

Trinxs
Senior Technical Sales Consultant - PAC
Reply

Link copied. Please paste this link to share this article on your social media post.

RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2023-07-21 01:57 AM

In response to Trinxs1
1 Like
0
2208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-07-21 01:57 AM

Hi Trinx,

 

The limitation of 100.000 Items refers to the size of the data-dictionary. As M580 has only 1 data-dictionary, shared by both BMENUA's they will have both this same limitation. So any CPU with more than 100.000 Items in the data-dictionary will be impossible even using multiple BMENUA's.

R.Roozee
Sr Solution Architect (SAE Master)
Reply

Link copied. Please paste this link to share this article on your social media post.

SESA668293
SESA668293 Cadet
Cadet

Posted: ‎2024-05-30 09:57 AM

1 Like
1
1420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-30 09:57 AM

Hi,

I have a question from a customer about using OPCUA cards with a redundant PLC Can you help me answer it because i found nothing.

Today, it is possible to configure an IP address for them on api A and api B.
However, it is not possible to configure a virtual address that corresponds to the OPCUA card on the active PLC (as is done on the cpu or noc).
This makes things more complicated on the SCADA side because you have to manage which board the IO server should communicate on.

Is this a planned feature or other solution ?

Myrtille SAE

Reply

Link copied. Please paste this link to share this article on your social media post.

THLA
THLA
Cadet

Posted: ‎2025-01-28 12:45 AM

In response to SESA668293
0 Likes
0
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-28 12:45 AM

Following this thread. I have the same issue. 
If we have a switchover on "PLC A" from Master to Standby on a PLC, the SCADA does not follow as long as the I/O device "PLC A" is still active. Since "PLC A" now becomes the standby PLC, you loose WRITE permission to the PLC from SCADA. Until either "PLC A" becomes master again, or until it actually becomes inavailable for communication and the SCADA system switches over to standby. 

For reference I am using PlantSCADA 2023 R2 and HotStandby M580 PLCs with BMENUA OPC cards.

Reply

Link copied. Please paste this link to share this article on your social media post.

leo_arabolu
leo_arabolu
Cadet

Posted: ‎2025-02-27 07:17 AM

0 Likes
0
494
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-27 07:17 AM

Hy to all.

 

Same issues using Plant SCADA 2023 v8.40 Update 13 and HSBY M580 PLC's with BMENUA0100 OPC UA cards. 

Any suggestion or solution will be appreciated.

Thanks in advance.

Reply

Link copied. Please paste this link to share this article on your social media post.

KJBER
Ensign KJBER
Ensign

Posted: ‎2025-02-28 03:20 AM

0 Likes
0
472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-28 03:20 AM

You need to monitor the service level from both BMENUA0100 cards, and script a "changeover" in the scada system to always read/write to server that is connected to Primary PLC. That is the modules that has service level 255 (above 200). The standby will have service level 199 if it is standby and ready.

 

KJBER_0-1740741513469.png

KJBER_1-1740741528826.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

rkardos
rkardos
Cadet

Posted: ‎2025-03-11 06:41 AM

0 Likes
0
344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-11 06:41 AM

I've had issues losing communication with the NUA module in the standby rack in testing, haven't used it in a production environment.

 

You might have a problem having sufficient rack power with all those network modules. I couldn't find a power supply large enough to have 2 x NUA + 2 x NOC modules.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login