Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

BMENOR2200.2 Module Configuration in Control Expert 16.0

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • BMENOR2200.2 Module Configuration in Control Expert 16.0
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Start a Topic
Solved
Valentinaprt
Valentinaprt Contributor
Contributor

Posted: ‎2025-03-18 12:40 PM . Last Modified: ‎2025-03-18 01:23 PM

0 Likes
2
1277
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 12:40 PM . Last Modified: ‎2025-03-18 01:23 PM

BMENOR2200.2 Module Configuration in Control Expert 16.0

How can I enable the control ports if I can't find them in the options displayed by the module when connecting to Control Expert 16.0? The options mentioned in the user manual for enabling control ports and assigning the IP address of control ports in Control Expert 16.0 are not found.

 

ValentinaPortilla_0-1742326773381.png

This is the information in the WebServer, just the IP adresses:

ValentinaPortilla_0-1742328178717.png

 

 

Attachments
Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Siddiqui
Siddiqui Contributor
Contributor

Posted: ‎2025-03-18 11:05 PM

1 Like
1
1238
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 11:05 PM

Hi @Valentinaprt ,

 

Please verify that you are using the step3 version of the BMENOR2200.3 inside your configuration because this version comes with control ports, as shown in the snapshot below.

Siddiqui_0-1742364147373.png

From your snapshot, I noticed that you are using the Step 2 version of the BMENOR module, not the Step 3 version.

 

Make sure that the HF is installed inside the ECE V 16.0 for the Step 3 BMENOR module. The HF can be found in the following link.

https://www.se.com/fr/fr/download/document/ControlExpert_V160_HF005/

 

The options to enable the control ports are inside the DTM under the following section:

Siddiqui_1-1742364147378.png

 

NOTE: The two control ports in the front do not support RSTP or other redundancy protocols. Please design your network appropriately and ensure there are no loops that can create a storm.

 

Best Regards,

MWS 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Valentinaprt
Valentinaprt Contributor
Contributor

Posted: ‎2025-03-19 06:38 AM

In response to Siddiqui
1 Like
0
1222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-19 06:38 AM

Hi @Siddiqui , thank you for your response! It was very helpful! You were right. I didn't have the Step 3 version of the BMENOR module in my options, and that was a problem. Installing the HF inside the ECE V 16.0 for the Step 3 BMENOR module was enough to access the control port configuration. Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Siddiqui
Siddiqui Contributor
Contributor

Posted: ‎2025-03-18 11:05 PM

1 Like
1
1239
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 11:05 PM

Hi @Valentinaprt ,

 

Please verify that you are using the step3 version of the BMENOR2200.3 inside your configuration because this version comes with control ports, as shown in the snapshot below.

Siddiqui_0-1742364147373.png

From your snapshot, I noticed that you are using the Step 2 version of the BMENOR module, not the Step 3 version.

 

Make sure that the HF is installed inside the ECE V 16.0 for the Step 3 BMENOR module. The HF can be found in the following link.

https://www.se.com/fr/fr/download/document/ControlExpert_V160_HF005/

 

The options to enable the control ports are inside the DTM under the following section:

Siddiqui_1-1742364147378.png

 

NOTE: The two control ports in the front do not support RSTP or other redundancy protocols. Please design your network appropriately and ensure there are no loops that can create a storm.

 

Best Regards,

MWS 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Valentinaprt
Valentinaprt Contributor
Contributor

Posted: ‎2025-03-19 06:38 AM

In response to Siddiqui
1 Like
0
1223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-19 06:38 AM

Hi @Siddiqui , thank you for your response! It was very helpful! You were right. I didn't have the Step 3 version of the BMENOR module in my options, and that was a problem. Installing the HF inside the ECE V 16.0 for the Step 3 BMENOR module was enough to access the control port configuration. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore