Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.
Search in
Please select a country to continue with beta search.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 06:55 PM
Hi All,
I have the configuration with M580 HSBY and STB Distibuted IO via the RSTP protocol but the customer asked to add the Modbus RTU/Serial Protocol.Tried to add the BMXNOM0200 but can't. What module should I use in this case? Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 11:31 PM
Hello Godfrey,
I think you can offer EGX150 or Panel server to be a gateway and be connected to CRA service port which will guaranty the redundant connection between the two CPUs
But please consider the following:
The speed of service port is 5 Mbps so please don`t add many gateways (my recommendation 4 or 5 gateways and each gateway handle 7 RS485 devices)
Maybe the main controller will loss the communication with RS485 devices when the system transfer between CPUs for 3 or 5 second depends on number of requests and devices , and incase the system controls in RS485 devices you will need to increase the devices watchdog or timeout a little bit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 11:52 PM
Godfrey
You can only add the BMXNOM0200 to a drop rack not the CPU racks.
The alternative assuming you require Modbus RTU RS485 protocol is to use a modbus ethernet to modbus serial gateway such as a panel server 600.
Trinxs
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 11:31 PM
Hello Godfrey,
I think you can offer EGX150 or Panel server to be a gateway and be connected to CRA service port which will guaranty the redundant connection between the two CPUs
But please consider the following:
The speed of service port is 5 Mbps so please don`t add many gateways (my recommendation 4 or 5 gateways and each gateway handle 7 RS485 devices)
Maybe the main controller will loss the communication with RS485 devices when the system transfer between CPUs for 3 or 5 second depends on number of requests and devices , and incase the system controls in RS485 devices you will need to increase the devices watchdog or timeout a little bit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 11:52 PM
Godfrey
You can only add the BMXNOM0200 to a drop rack not the CPU racks.
The alternative assuming you require Modbus RTU RS485 protocol is to use a modbus ethernet to modbus serial gateway such as a panel server 600.
Trinxs
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-04 03:08 PM
Thanks guys
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.