Hi All,
I have the configuration with M580 HSBY and STB Distibuted IO via the RSTP protocol but the customer asked to add the Modbus RTU/Serial Protocol.Tried to add the BMXNOM0200 but can't. What module should I use in this case? Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 11:31 PM
Hello Godfrey,
I think you can offer EGX150 or Panel server to be a gateway and be connected to CRA service port which will guaranty the redundant connection between the two CPUs
But please consider the following:
The speed of service port is 5 Mbps so please don`t add many gateways (my recommendation 4 or 5 gateways and each gateway handle 7 RS485 devices)
Maybe the main controller will loss the communication with RS485 devices when the system transfer between CPUs for 3 or 5 second depends on number of requests and devices , and incase the system controls in RS485 devices you will need to increase the devices watchdog or timeout a little bit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 11:52 PM
Godfrey
You can only add the BMXNOM0200 to a drop rack not the CPU racks.
The alternative assuming you require Modbus RTU RS485 protocol is to use a modbus ethernet to modbus serial gateway such as a panel server 600.
Trinxs
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 11:31 PM
Hello Godfrey,
I think you can offer EGX150 or Panel server to be a gateway and be connected to CRA service port which will guaranty the redundant connection between the two CPUs
But please consider the following:
The speed of service port is 5 Mbps so please don`t add many gateways (my recommendation 4 or 5 gateways and each gateway handle 7 RS485 devices)
Maybe the main controller will loss the communication with RS485 devices when the system transfer between CPUs for 3 or 5 second depends on number of requests and devices , and incase the system controls in RS485 devices you will need to increase the devices watchdog or timeout a little bit.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-28 11:52 PM
Godfrey
You can only add the BMXNOM0200 to a drop rack not the CPU racks.
The alternative assuming you require Modbus RTU RS485 protocol is to use a modbus ethernet to modbus serial gateway such as a panel server 600.
Trinxs
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-02-04 03:08 PM
Thanks guys