Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

M340 Firmware update questions

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • M340 Firmware update questions
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Start a Topic
Solved
pwbridgeman
pwbridgeman
Explorer

Posted: ‎2023-01-22 05:59 PM

0 Likes
3
5685
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-22 05:59 PM

M340 Firmware update questions

Hello,
I have a couple of questions regarding updating the firmware on a M340 CPU. (I have read the manual for the processor and also cybersecurity documents but cannot find this info...)
First, does the latest FW version contain all of the improvements/fixes from the previous releases or do they all have to be installed? For example, I have a M340 at SV 02.50 and I have installed SV 03.50. Am I good there or do I need to install 02.60, 02.70, up to the latest?
Second, regarding that same CPU that I have updated from 02.50 to 03.50... Should I now be able to disable ftp/http access to increase security? I know that the SV has to be at least 2.60 in order to do this, but does updating past this version qualify? The reason I ask is that after updating the fore-mentioned CPU which now shows processor version 03.50-7 under the cpu information tab, when trying to disable ftp/http access I get the following error -
"This CPU (BMX P34 2020) or it's version (V 02.30) doesn't support the security services. Enable all fields(ftp/http) or replace the current CPU"

See attached pics.


Any insight on this is greatly appreciated! Thanks in advance.

Attachments
Labels
  • Labels:
  • 01. Modicon M340 PAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
AlastairF
AlastairF Leader
Leader

Posted: ‎2023-01-24 03:58 PM

0 Likes
1
5681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 03:58 PM

Did you update the CPU version in Control Expert?
You need to ensure the selected CPU version is at same level as the FW on the CPU hardware.

See attached picture.

 

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
AlastairF
AlastairF Leader
Leader

Posted: ‎2023-01-24 03:58 PM

0 Likes
1
5682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 03:58 PM

Did you update the CPU version in Control Expert?
You need to ensure the selected CPU version is at same level as the FW on the CPU hardware.

See attached picture.

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

pwbridgeman
pwbridgeman
Explorer

Posted: ‎2023-01-24 04:46 PM

In response to AlastairF
0 Likes
0
5676
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-24 04:46 PM

Hi AlastairF,

  Thank you for the reply. Yes, that is what I was missing. When I originally posted this question Sunday night it somehow got marked as spam and did not post to the forums. The next morning I contacted tech support and the engineer told me the same thing you just posted.

Thanks again for the reply.

Paul

Reply

Link copied. Please paste this link to share this article on your social media post.

bestdiamondleve
bestdiamondleve
Explorer

Posted: ‎2023-03-20 08:19 AM

0 Likes
0
5501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-20 08:19 AM

Has Control Expert's CPU version been updated?
Ensure the CPU hardware FW is at the same level as the selected CPU version.
Please see attached.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore