Posted: 2022-12-20 10:57 PM
Hello
I need your support on how can we send data from M221 PLC to Cloud.
There several PLCs located in different locations and they have access to internet through a VSAT, The objective is collect data from the different PLCs to a cloud.
What is the best solution ?
Is there any SE cloud service dedicated for this type of solution ?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-12-21 04:03 PM
Hi
No SE cloud service.
Best way to get M221 connected to a cloud service would be using the Teltonika RUT240 Gateway
Regards
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-12-21 07:46 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-12-22 02:40 AM
He Steve
Thanks for your reply, is there a support on how to configure the gateway ?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-27 08:38 AM
If you have an Internet connection you could use TM172SIG as easy programmable cloud gateway from SE. The TM172SIG could read the values via Modbus RTU / RS485 out of the TM221. IF you need also a modem you could use directly a modem solution like described before.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-27 01:52 PM
Hi
I have a how to document if you require one
Regards
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-02-28 12:54 AM
Yes, would be great, thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-02 07:45 AM
buenos dias estimado sr, estamos interesados en utilizar en nuestros cursos aplicaciones en la nube sencillas utilizando el M221
BAJO TCP /IP, MODBUS nos podría orientar al respecto
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-02 07:20 PM
You have been emailed
Regards
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-05-16 10:17 AM
Link copied. Please paste this link to share this article on your social media post.