Posted: 2025-05-19 04:43 AM
Hi,
I need to understand how to find/configured in Control Expert for M580 whether Modbus Communication with any Modbus Slave device is working or has stopped ?
Is there any fail/error bit/code to sense this ?
Right now as values gets transferred between M580 and PSO over Modbus TCP, the value gets stuck in PSO if downstream devices stop communication with M580 for any reason.
Is it also possible to convert this value automatically to "ZERO" in case the Modbus communication with field device breaks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-19 08:50 PM
Good day,
1. Yes you can monitor the Freshness bit in the Device DDT variable which is created when adding modbus device.
Secondly to set the values to 0 if comms fail, open the NOC/CPU in the DTM browser and go to the Request settings of the modbus device. Each request can be set to 'Set to Zero' under the Last Value column.
Regards,
Hennie Smith
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-19 10:05 PM
1. I have implemented communication fault/normal status detection using the 'Gest' value from Read_Var.
The second word of the GEST value is 0 when communication is normal, and any value greater than 0 indicates an error.
Please refer to the attached PDF file for more details, and feel free to contact us if you have any questions.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-18 01:18 AM
Hi,
Thanks a lot for your reply.
1) For what you have shared with NOC card, is same feature available with NOM card as well as we are polling around 10 Nos. of Modbus Serial devices using NOM card in M580.
2) Also, we have observed randomly data of MFM(Multi Function Energy meter)getting stuck while using READ VAR block to poll MFM(Multi Function Energy meter) for 10 Nos. MFMs in one single loop.
What is further way to diagnose such issues i.e. how to understand if query length is too high or if we need to increase delay period between 2 polls of Modbus - this is for Modbus Serial(RTU) communication only. Does M580 inherently supports protocol tracing ?
Looking forward to your support.
Thanks & Regards
Ruchir Somani
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-18 01:20 PM
Hello Ruchir,
There are some key concepts to take into account when implementing READ_VAR function.
First, you must specify the timeout period in the third register of the GEST array. A value of 5 means 500 ms and should normally be enough.
Please note that the NOM is configured with its own default answer delay (10 * 100 = 1000ms) and 3 retries. The timeout set in the third register should be greater than the answer delay time X number of retries.
You can reduce the default answer delay and set the number of retries to 0 to speed out the process if needed.
Second, it is recommended to expose the READ_VAR EN-ENO pins, then negate the EN pin and connect bit 0 (Active) of the first GEST register to it. This will disable the block call when a communication session is active.
Third, for serial communication avoid using more than one READ_VAR in parallel for the same NOM channel. If you are polling several devices on the same line, you need to manage the order in which they are called. For this purpose I am attaching a DFB based on DATA_EXCH function which is designed to manage as many devices as required sequentially and cyclically by proper parametrization. This all-in-one solution DFB requires no extra code. However, I do not have it documented in English so you will probably need some help to implement it. If you are interested in testing it, I can provide some simple examples.
Best Regards.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-06-18 08:31 PM
1. The file I attached was applied to the BMXNOM card. Therefore, the same configuration can be applied to the NOM card as well.
2. Does the freezing issue occur when communication is lost with the device connected to the BMXNOM0200?
If so, please refer to the following link for more information:
https://community.se.com/t5/Modicon-PAC-Forum/BMXNOM0200-READ-VAR/m-p/487416#M1274
3. If the issue is not related to point 2, please increase the polling interval at the READ_VAR EN input as shown in the attached image.
4. Compare the GEST values between normal and abnormal communication cases.
5. If you have any further questions, feel free to reply.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of