Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Channel fault or lower threshold range alarm for BMXAMI0810 analog module.

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Channel fault or lower threshold range alarm for BMXAMI0810 analog module.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Start a Topic
AvinashPatil
AvinashPatil Explorer
Explorer

Posted: ‎2022-09-19 10:47 PM

1 Like
4
3723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-19 10:47 PM

Channel fault or lower threshold range alarm for BMXAMI0810 analog module.

I have BMXAMI0810 analog module with 0-10v signal type configuration (0-10000 scaling). I want to check channel fault alarm or lower threshold range alarm for the same. As sensor is 0-10v type so when I remove the power plug from sensor end it gives 0 value to PLC. As per module data sheet, lower threshold tolerance range is -1 to -1000. when signal is -1 or less than then only will receive lower range alarm. Any other way to test the same or particular channel fault alarm. Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
AlastairF
AlastairF Leader
Leader

Posted: ‎2022-09-22 01:54 PM

1 Like
2
3682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-22 01:54 PM

You can adjust the low range threshold value up to a maximum of 0 for the 0..10V range.

If your normal working signal range is above 0 then I would just write some logic to look for values below the working range (with a time delay).

Otherwise use a 0..10V:4..20mA signal conditioner and set the module to 4..20mA. A wire break will provide an alarm.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Robert_Willis
Robert_Willis Troubleshooter
Troubleshooter

Posted: ‎2022-09-22 02:13 PM

0 Likes
0
3679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-09-22 02:13 PM

1. Which platform are you using this with Modicon M340, M580 or Quantum? 

2. Is the BMXAMI0810 configured with Topological Addressing or Device DDT? The Modicon M580 supports both Topological and Device DDT in the local racks and only Device DDT the ERIO "Ethernet Remote I/O Drops".

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

andreychukvolodymyr
andreychukvolodymyr
Explorer

Posted: ‎2023-06-09 08:19 PM

In response to AlastairF
0 Likes
0
3430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-09 08:19 PM

is it dangerous to changed polarity for channel + & - ? can it damaged the channel? output voltage from channel is 0 volts. I do not have possibility to check how channel is configurated. 

if no voltage from channel , but from sensor signal in 4-20mA.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

andreychukvolodymyr
andreychukvolodymyr
Explorer

Posted: ‎2023-06-09 08:20 PM

In response to AlastairF
0 Likes
0
3430
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-06-09 08:20 PM

is it dangerous to changed polarity for channel + & - ? can it damaged the channel? output voltage from channel is 0 volts. I do not have possibility to check how channel is configurated. 

 

if no voltage from channel , but from sensor signal in 4-20mA.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore