Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Can't connect Modicon M580 with OFS OPC

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • Can't connect Modicon M580 with OFS OPC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Modicon PAC Forum
Start a Topic
datajaya_ap
datajaya_ap
Explorer

Posted: ‎2024-06-04 02:08 AM

0 Likes
5
2923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-04 02:08 AM

Can't connect Modicon M580 with OFS OPC

Hi All,

 

We have 2 archestra machines dedicated for Simulation and Production. one of machine which has installed the OFS not able to connect with the Modicon M580. the error log is mentioned that  if the status is MISSING. anyone can help which configuration is missing in the Production environment ? there is no issue with simulation environment. 

 

FYI, i have uploaded the OFS configuration from simulation to the production. 

Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • Tags:
  • OFS
  • OPC Factory Server
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
PatrickVanDijk
PatrickVanDijk
Troubleshooter

Posted: ‎2024-06-04 11:54 PM

0 Likes
3
2890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-04 11:54 PM

Can you specify the exact OFS error? What is missing? Is it missing the PLC in the network, or is it missing a valid OFS configuration?
Also, what do you mean by having "uploaded the OFS configuration..."? Did you only copy the configuration files from one machine to the other? I don't think that will do the trick.

Please run the OFS Configuration Tool and verify all settings of the PLC entries. Then press the GREEN save button to activate the configuration.

Last thing: please be aware of some issues in the newest releases of OFS. v3.63 SP2 has a serious memory leak (I witnessed 10MB RAM increase per hour in some cases), and v3.63 SP3 may want to try to connect to the internet in some cases.

Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
MatthewM
Mentor

Posted: ‎2024-06-05 02:41 PM

0 Likes
0
2872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-05 02:41 PM

If your error looks something like this:

06/06 09:37:45 235ms : NETMAN : MBT:192.168.20.20 Status MISSING (Error = afe20006h) (uid: 20436)

it means it can't see the PLC.  Check the IP address is correct using OFS Configuration Tool on the server that is not working, and verify it is correct and pingable.

Reply

Link copied. Please paste this link to share this article on your social media post.

datajaya_ap
datajaya_ap
Explorer

Posted: ‎2024-06-22 02:17 AM

In response to PatrickVanDijk
0 Likes
2
2769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-22 02:17 AM

Thanks for your response. the issue was solved. this is because the network still blocked. after the network team open the firewall, the issue has solved
About the issues in the newest releases. I am used the OFS v.3.63.4904. this version is SP2 or SP3 ? because right now, i have issue some time the connection is broken between OIGateway and OFS. then i need to restart the OFService

Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
MatthewM
Mentor

Posted: ‎2024-06-24 08:40 PM

In response to datajaya_ap
1 Like
0
2762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-24 08:40 PM

Build 4904 is 3.63 SP2.  Build 4905 is 3.63 SP3.

Reply

Link copied. Please paste this link to share this article on your social media post.

PatrickVanDijk
PatrickVanDijk
Troubleshooter

Posted: ‎2024-06-24 11:16 PM

In response to datajaya_ap
0 Likes
0
2745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-24 11:16 PM

Needing to restart OFS periodically sounds like the memory leak issue I mentioned earlier. With this issue OFS will consume more and more RAM until the 4GB limit is reached. Then it will stop and hang or crash.

Try and test v3.63 SP3 (build 4905). If this does not work for your application, then go back to an earlier version if possible. Be aware that earlier versions do not support all current Windows versions (like Windows 11).

Reach out to Support if none of the options work for you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore