Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

64-bit Float Modbus Register

Modicon PAC Forum

A forum for topics related to the scope of Modicon PAC offers and ecosystem along the whole lifecycle: Modicon M580 and 340, EcoStruxure Control Expert, EcoStruxure Process Expert (Unity Pro) and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon PAC Forum
  • 64-bit Float Modbus Register
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Trinxs1
Trinxs1 Leader
19
YONGHO-KIM
YONGHO-KIM Mentor
10
ciupol
ciupol
9
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Modicon PAC Forum
Start a Topic
Solved
alekseib
alekseib
Contributor

Posted: ‎2022-12-10 06:34 AM

0 Likes
8
9864
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-10 06:34 AM

64-bit Float Modbus Register

How to read 64-bit Modbus register (4xIntegers) and convert it to understandable value in Control Expert?

Labels
  • Labels:
  • 02. Modicon M580 ePAC
  • 06. EcoStruxure Control Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MichaelWisesa
MichaelWisesa
Contributor

Posted: ‎2022-12-12 07:06 AM

2 Likes
1
9778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-12 07:06 AM

I did something like this:

MichaelWisesa_0-1670857490786.png

1st is to read the data in words, or you can use byte as word instruction

2nd to split the sign, exponent, and mantissa from 64 bit format

3rd to rearrange the sign, exponent, and mantissa to 32 bit format

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
wdustman
wdustman Explorer
Explorer

Posted: ‎2022-12-10 09:19 AM

0 Likes
0
9858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-10 09:19 AM

Assuming you know how to receive the information using the DTM browser (if not let me know). Use a move command to move the modbus information received to any free %MW location. Make a new variable (LREAL) starting at that same %MW. You can then use that variable and view the value.  [I'm on mobile, so let me know if that is enough to help, if not I can provide full details Monday].

Reply

Link copied. Please paste this link to share this article on your social media post.

MichaelWisesa
MichaelWisesa
Contributor

Posted: ‎2022-12-10 04:49 PM

1 Like
1
9834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-10 04:49 PM

Problem is Control Expert/Unity Pro doesn't support 64 byte float or double float. We need to translate 64 byte float to 32 byte float manually (create logic) to workout the exponent and mantissa, and lose some precision.

 

These websites helps you breakdown the 2:

https://www.binaryconvert.com/convert_double.html

https://www.binaryconvert.com/convert_float.html

https://ryanstutorials.net/binary-tutorial/binary-floating-point.php

 

Essentially you need to remap the exponent from 11 bit to 8 bit and mantissa from 52 bits to 23 bits

Reply

Link copied. Please paste this link to share this article on your social media post.

alekseib
alekseib
Contributor

Posted: ‎2022-12-12 04:57 AM

In response to MichaelWisesa
0 Likes
0
9788
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-12 04:57 AM

I wrote 4 INTEGERS by bits to 1 STRING. By using LEFT_INT, MID_INT and RIGHT_INT function blocks received sign, exponent and mantissa. How to convert them from STRING to numbers (int, dint, real)?

Reply

Link copied. Please paste this link to share this article on your social media post.

MichaelWisesa
MichaelWisesa
Contributor

Posted: ‎2022-12-12 07:06 AM

2 Likes
1
9779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-12 07:06 AM

I did something like this:

MichaelWisesa_0-1670857490786.png

1st is to read the data in words, or you can use byte as word instruction

2nd to split the sign, exponent, and mantissa from 64 bit format

3rd to rearrange the sign, exponent, and mantissa to 32 bit format

 

Reply

Link copied. Please paste this link to share this article on your social media post.

riyat.danisman
riyat.danisman
Explorer

Posted: ‎2024-08-09 05:20 AM

In response to MichaelWisesa
0 Likes
0
6699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-09 05:20 AM

Hello,
I'm wondering about something. There should be 4 words in total for 64 bits, but you did it with "Double2_I, Double3_I, Double4_I". Where did you use "Double1_I"? I couldn't see it in the photo.
I'm trying to read a "wh" value from the energy analyzer from the modbus map in order;
801
802
803
804
with a total of 4 INT/Holding Registers.

Does it have to be used as;
Double1_I : 801
Double2_I : 802
Double3_I : 803
Double4_I : 804
?

Reply

Link copied. Please paste this link to share this article on your social media post.

PetrBC
PetrBC
Contributor

Posted: ‎2025-06-13 05:46 AM

1 Like
0
4170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-13 05:46 AM

If you're looking for a simple, elegant solution, it is there. At output, you connect WORD_AS_REAL.

(*Converting block - word of 64bit REAL to word of 32bit REAL*)
(*left are outputs word, right are inputs word*)
(*MW64 = most word of 64bit real*)
(*UW64 = upper word of 64bit real*)
(*BW64 = bottom word of 64bit real*)
(*LW64 = least word of 64bit real, not used by converting*)
(*HW32 = high word of 32bit real*)
(*LW32 = low word of 32bit real*)

HW32.15:=MW64.15;(*sign*)

HW32.14:=MW64.14;(*highest exponent*)
HW32.13:=MW64.10;(*copying of exponent*)
HW32.12:=MW64.9;
HW32.11:=MW64.8;
HW32.10:=MW64.7;
HW32.9:=MW64.6;
HW32.8:=MW64.5;
HW32.7:=MW64.4;

HW32.6:=MW64.3;(*copying mantissa*)
HW32.5:=MW64.2;
HW32.4:=MW64.1;
HW32.3:=MW64.0;
HW32.2:=UW64.15;
HW32.1:=UW64.14;
HW32.0:=UW64.13;

LW32.15:=UW64.12;(*copying mantissa*)
LW32.14:=UW64.11;
LW32.13:=UW64.10;
LW32.12:=UW64.9;
LW32.11:=UW64.8;
LW32.10:=UW64.7;
LW32.9:=UW64.6;
LW32.8:=UW64.5;
LW32.7:=UW64.4;
LW32.6:=UW64.3;
LW32.5:=UW64.2;
LW32.4:=UW64.1;
LW32.3:=UW64.0;
LW32.2:=BW64.15;
LW32.1:=BW64.14;
LW32.0:=BW64.13;

Reply

Link copied. Please paste this link to share this article on your social media post.

ag56
ag56
Explorer

Posted: ‎2025-06-17 08:50 AM

0 Likes
0
4088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-17 08:50 AM

Hello alekseib, use attached DFB to convert the two most significant registers of a long real into 32 bit real.

The reduced precision of the result will be Negligible in most cases.

Attachments
LREAL_HIGH_TO_REAL.zip
Reply

Link copied. Please paste this link to share this article on your social media post.

lucky77
lucky77
Explorer

Posted: ‎2025-10-30 05:04 AM

0 Likes
0
2820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-30 05:04 AM

Good morning, everyone. I'm not sure if this is the right place to ask my question, but I'm having a problem with a totalizer read via Modbus TCP. I'm using the DINT_TO_REAL block, which allows me to read the data up to a certain digit. After that, the data is read as a negative value, and I've already identified the error: the data should be read as DINT_TO_LINT, since it's a full 64-bit value. My question is, how can I read these registers and transfer them to four 16-bit memories or two 32-bit memories so I can combine them and read the final total? I'm using an M340 CPU and the EcoStruxure Control Expert 14 software. Please excuse my English, as I'm using a translator.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore