Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Redundant in rack M580 Redundant Master modules?

Modicon Ideas & new features

Have ideas on how to improve Modicon? Please share and get votes from Community to influence development efforts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Modicon Ideas & new features
  • Redundant in rack M580 Redundant Master modules?
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • 06. EcoStruxure Control Expert 44
  • 02. Modicon M580 ePAC 22
  • 05. Networking & Communication 12
  • 01. Modicon M340 PAC 8
  • 03. Modicon PAC Safety 3
  • 04. Modicon X80 IO 3
  • 12. Other 2
  • 08. Tools & Resources 1
  • 07. Modicon PAC Legacy 1
  • 09. Surveys 1
  • 10. Australia 1
Idea Statuses
  • Submitted 49
  • Needs more info 0
  • Under consideration 2
  • Accepted 2
  • Declined 0
  • To be deleted 0
  • Delivered 3
Related Products
Thumbnail of Modicon M580
Schneider Electric
Modicon M580
7
Thumbnail of EcoStruxure™ Control Expert
Schneider Electric
EcoStruxure™ Control Expert
6
Thumbnail of Modicon M340
Schneider Electric
Modicon M340
2
Load more
Completed Ideas
  • EcoStruxure Control Expert - DTM Update Tool

  • The ability to access DTMs in a different subnet via the DTM browser

  • [networks] Should we implement PRP in our network offer?

View All
Top Liked Authors
User Likes Count
Trinxs1
Commander Trinxs1 Commander
6
Snacky
Ensign Snacky
5
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
5 Likes

Redundant in rack M580 Redundant Master modules?

Status: Under consideration Submitted by Commander Trinxs1 Commander on ‎2019-10-22 12:59 AM
6 Comments (6 New)
 

How do you wish to implement redundant ERIO networks?

  1. Would you want a double ring topology?
    • Protocols - HSR, DLR, RSTP
    • Module - dual ring connections on single module, single ring connection on two modules
    • See Choice A
  2. Would you want a double network topology?
    • Protocol - PRP
    • Dual network with same information sent over both networks
    • More expense
    • See Choice B
  3. Would you want a separate backbone topology?
    • Protocol - up to installer
    • Dual connections to ethernet backbone managed by IT 
    • Third party protocols selected by user.
    • Must comply with basic requirements
    • See Choice C

Revised offer (2nd March 2020):

1. Single module with single connections to two separate ring / star  networks using PRP.

2.  Hot standby system with single connection for each CPU to two separate networks with two separate modules in each drop.

 

In each architecture PRP is primarily the network protocol.  The network is constructed using third party switches with some requirements to be specified in the design.

 

In the system proposed how many drops are required?

1. 32 drops

2. 64 drops

3.  more than this?  how many?

 

Tags (3)
  • Find more ideas tagged with:
  • ERIO
  • redundancy
  • RFF
Labels (3)
See more ideas labeled with:
  • 02. Modicon M580 ePAC
  • 05. Networking & Communication
  • 09. Surveys
Comment

Link copied. Please paste this link to share this article on your social media post.

  • Back to Idea Exchange
  • Previous
  • Next
6 Comments
Trinxs1
Commander Trinxs1 Commander
Commander
‎2019-10-22 01:00 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-10-22 01:00 AM

Currently the PME PXM 0100 module  supports the following 3 basic architectures:

-Standalone PLC – PXM in Local Rack

-Standalone PLC – PXM in Remote Rack

-HSBY PLC – PXMs in Local Rack

 

For future development our work with ProSoft will take into account the PXM additional redundancy modes enhancement listed below and we need your feedback to know the business case of these new functionalities.

 

Could you send me your feedback (Customer name, architecture targeted, PXM & CPU number targeted with these new functionalities)?

 

The table below summarizes the various configurations, (both existing and proposed)

clipboard_image_0.jpeg

clipboard_image_1.png

 

 

SESA52376
SESA52376 Cadet
Cadet
‎2019-12-06 05:38 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2019-12-06 05:38 AM

A and B have my preference.

I think PRP is on the winning hand, but a solution without extra switches is not bad eather.

sujith.k
sujith.k
Cadet
‎2022-04-10 09:45 PM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2022-04-10 09:45 PM

I have few question on PRP feature

1. Which PLC supports PRP protocol?

2. in the choice B(PRP), M580 NOC module generates PRP packets? If yes, which module support PRP?

3. I have Modbus TCP device which supports PRP. How to test PRP feature with Modicon PLC?

Trinxs1
Commander Trinxs1 Commander
Commander
‎2022-04-28 05:06 PM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2022-04-28 05:06 PM

My apologies I have been away for a few weeks.

1.  M580 in a release later in 2024 or possibly 2025 schneider will have modules that support PRP.  This is part of the dual redundant ethernet remote IO network.  It will occur in stages but the first will provide drop modules in the rack that support PRP and at the CPU end there may be third party modules and eventually M580 PRP modules that sit in the rack.

2.  The BMENOC module at this stage will not support PRP.  The intent for PRP is to effectively provide zero communications down time between the M580 CPU and the remote IO X80 racks.  It may be a feature in the future if there is sufficient demand but this need must be made known to your Schneider account managers and technical support people so we can try to drive the road map of development.

3.   The PRP modules will allow other protocols to co-exist.  Its aim is to ensure that two sets of the same ethernet packet are sent to each destination and at the destination the recipient rejects duplicated packages.  To test you would need to monitor the update rate of the messages at the modules.  Typically, this should be the same irrespective if both or one of the network pathways is operational. 
To test break a network to see if the update rate changes. I am deliberately vague at the moment as the equipment has not been released, I cannot provide exact details. 

4.  At the CPU end we will have the start of the PRP network.  Initially this will be with a Hirschmann RED25 - which provides RSTP to PRP (Port PRP-A and port PRP-B) at the other end of the communication i.e. the drop racks there will be a new full length CRA module which will also have (Port PRP-A and port PRP-B).  If the system is a hot standby CPU system, it may also be possible to have two new PRP CRA modules in one drop rack.  In this case one module will be the primary module and the other will be a standby module. 

Trinxs1
Commander Trinxs1 Commander
Commander
‎2023-03-09 04:10 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2023-03-09 04:10 AM
Status changed to: Under consideration

Field testing for the dual ethernet remote io network system will commence in 2023.

RQ
RQ
Cadet
‎2024-02-19 11:16 PM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2024-02-19 11:16 PM

Can you Please share the dual ethernet remote IO's architecture 

Comment
Preview Exit Preview

never-displayed

Hint:
@ links to members, content
 
  • Back to Idea Exchange
  • Previous
  • Next
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore