Is there an upgrade map for this family of meters?
Why would there be a maximum of 10 successful upgrades for version 1.6.0? What does this mean?
Link copied. Please paste this link to share this article on your social media post.
The restriction of firmware upgrades is maximum to 10 for only MID models (PM5111, PM5331.PM5341) and it is MID certification requirement.
For Non MID models, the update is not restricted but firmware update log is restricted to 10. Only last 10 upgrades will be listed in the log.(FIFO)
Hope this is clear.
Link copied. Please paste this link to share this article on your social media post.
Hi Martin, what document are you looking at?