Hi All,
I would like to check if anyone have came across PM8240 auto reboot approx ever 2 minutes when network cable is plug into the meter with the other end to the network switch.
Currently I have install 8 numbers of PM8240, but only one of then is giving me this problem.
Few test I have conducted :
1. Laptop direct connection to the meter >>> No Issue
2. Connected the existing network cable to my laptop and ping other device... >> No Issue
Please advise.
Regards
Andrew LOH
Posted: 2016-07-04 11:18 PM
Link copied. Please paste this link to share this article on your social media post.
Hi Andrew,
I have seen this before, to start you need to be at a minimum firmware of 0001.002.14, do not upgrade to 0001.003.000 it has modbus issues. I believe a newer release will be available soon.
Regards,
Robert
Posted: 2016-06-26 07:04 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi Abon Chen ,
The firmware use is 0001.000.057
Regards
Andrew LOH
Posted: 2016-07-04 11:18 PM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hi Andrew,
I have a customer that is experiencing the same problem. Did you manage to find a solution for this issue?
Regards,
Theren
Posted: 2016-08-18 10:09 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Andrew
Hi Andrew, I would encourage you to contact tech support for assistance with this issue. They can walk you through removing of a diagnostic file on your device which can be analyzed to tell us exactly what is causing your resets. From there we can make suggestions on what course of action to take.
If you are using Modbus communications over your Ethernet connection then it is recommended you do NOT use version 1.000.057. As Robert indicated running 1.002.014 should be your target until the new release is available (I will check on timeline when the product prime is in the office).
But again if you want to know for sure what is causing your issues contacting tech support is the best option.
Brian
Link copied. Please paste this link to share this article on your social media post.
Hi Theren,
Yes... I manage to resolve the issue by upgrading the Firmware for the
power meter .
Regards,
Andrew LOH | Schneider Electric Singapore| Electrical Distribution
Application Center| Engineering, Assistant Manager
Phone: +65 6480 2270 | Fax: +65 6480 7800 | Mobile: +65 9750 5785
Email: andrew.loh@schneider-electric.com | Address: 10 Ang Mo Kio Street
65,#02-17/20 TechPoint, Singapore 569059
Link copied. Please paste this link to share this article on your social media post.
Hi Brian,
I have update the power meter firmware , and it is working fine now.
Thanks for the advise.
Regards,
Andrew LOH | Schneider Electric Singapore| Electrical Distribution
Application Center| Engineering, Assistant Manager
Phone: +65 6480 2270 | Fax: +65 6480 7800 | Mobile: +65 9750 5785
Email: andrew.loh@schneider-electric.com | Address: 10 Ang Mo Kio Street
65,#02-17/20 TechPoint, Singapore 569059
Link copied. Please paste this link to share this article on your social media post.
Could be the Modbus issue?
Link copied. Please paste this link to share this article on your social media post.
Thank you Andrew.
I think for my case, there is an issue with the hardware itself. The meter's screen is blank with the front LED flashing red and green. Customer cannot connect or ping the meter.