PM5111 pulse output configuration

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5111 pulse output configuration
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
sesa23104
sesa23104 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-05-22 06:49 AM

0 Likes
3
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-05-22 06:49 AM

PM5111 pulse output configuration

Did some one test the configuration of energy pulse ouptput of PM5111 with front panel device HIM?

It seems it is not possible to set the pulse output with the PM5111 HMI. When I set the device and save the modifications, the modifications are not saved

To do this on my product I have to use ION SETUP software.

Thanks for any feed back.

Philippe

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Anonymous user
Not applicable

Posted: ‎2015-05-25 01:08 AM

1 Like
2
1055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-05-25 01:08 AM

Hi Philipe Michon,

For present firmware (1.4.7 for MID meters, and 1.3.7 for non-MID meters), it can only be configured through ION Setup.

The factory has released a new firmware 1.6.0, which provides the possibility to configure through HMI. This new firmware version file will be available at site and Shopping Kiosk by this week.

Reply
sesa23104
sesa23104 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-05-25 11:48 PM

0 Likes
1
1056
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-05-25 11:48 PM

Hello Chen,

thanks a lot for your feed back. Just on more precision:

Is there only PM51xx affected by this issue or PM53xx and PM55xx have the same behaviour?

Best regards.

Philippe

Reply
Anonymous user
Not applicable

Posted: ‎2015-05-26 02:08 AM

0 Likes
0
1055
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-05-26 02:08 AM

Hello Philipe Michon,

It is applicable for PM5111, PM5331 and PM5341.

For PM5561, no this type of issue.

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of