I am unable to read data from SELEC MFM383A-C using RS 485 communication, getting error
I have configured correctly on serial settings and serial block. Refer below on block diagram and selec meter modbus register address.
|
2 (00000002 hex) |
The data address received by the slave is not an authorized address for the slave. |
Please provide solution .
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Try 30001 as the "FirstObj" parameter. Some Modbus devices can't agree on whether 0 or 1 is the first register.