One of our clients is facing issues with downloading power monitoring data from the ION8650 meters. Is there a way to connect meter directly with laptop to download the data? I see there is an optical port in the front, can that be used to connect the meter to a laptop and download monitoring data?
Link copied. Please paste this link to share this article on your social media post.
The optical port on the front is designed for an ANSI Type 2 optical probe--I believe any model on the market will do. I recommend one with a USB port and a magnetized head.
Once the drivers are installed on your laptop at the probe is connected, it will show up as a new serial port and you will be able to connect directly to the meter using ION Setup.
Link copied. Please paste this link to share this article on your social media post.
The optical port on the front is designed for an ANSI Type 2 optical probe--I believe any model on the market will do. I recommend one with a USB port and a magnetized head.
Once the drivers are installed on your laptop at the probe is connected, it will show up as a new serial port and you will be able to connect directly to the meter using ION Setup.