FAQ_ Toroids Compatible with Vigilohm Locators
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
>>> The criteria of selection is that Diameter of toroid > 1,4 x Diameter of cables bundle
Criterias such as maximum cross section area of conductors; maximum admissible current... do not apply to Vigilohm, since we measure differential currents (these criterias only apply if the toroids are used with Vigirex devices)
NB: A version in french of this document is available here.