there is a wrench icon blinking on the top corner of the analyzer. please advise how to troubleshoot.
Link copied. Please paste this link to share this article on your social media post.
The error 0101hex means language file mismatch with OS.
You need to upgrade the attached language file using the DLF3000 application.
Please note: Use the firmware file PM2xxxLL3000.fw if the OS version is v1.4.0 and below.
Or Use the firmware file PM2xxxLL4000.fw if the OS version is v1.5.0.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello @hammadjoufar ,
The wrench icon blinks when there is any diagnostic error noticed in the meter.
Please check the error code displayed on meter diag page (navigate to maint->diag->meter) and take necessary action from below description.
The list of error codes and short description of the error code.
1)0003 hex : RAM failure
2)0005 hex : NVRAM failure
3)0009 hex : RTC failure
4)0011 hex : Calibration failure
5)0021 hex : Clipping detected
6)0041 hex : Over running energy pulse output
7)0081 hex : Back up Ram/ V battery Fail
8)0101 hex :Language file incompatibility
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hi @Ramasamy_N
Thanks for the reply , I checked and found the error code is 0101 hex.
Please advise how to troubleshoot further.
Link copied. Please paste this link to share this article on your social media post.
The error 0101hex means language file mismatch with OS.
You need to upgrade the attached language file using the DLF3000 application.
Please note: Use the firmware file PM2xxxLL3000.fw if the OS version is v1.4.0 and below.
Or Use the firmware file PM2xxxLL4000.fw if the OS version is v1.5.0.
Regards,
Ramasamy N