In the datasheet it is stated that Current per Phase is measured but the current measurement is not available in the COMX.
We have only maximum current over demand, which I guess is the maximum current recorded by the EM over all 15 minutes windows since start-up.
Same thing for Voltage measurement, only L1-N voltage is shown, no measurement regarding L2, L3 and only Minimum
Is-it normal ?
Kind regards
Posted: 2017-09-21 02:19 PM
Link copied. Please paste this link to share this article on your social media post.
Hi Guillaume,
Please refer to chapter 5 of the EM4300 series user manual for a list of measurements accessible through the Com'X series gateway:
EN: PowerLogic™ EM4300 series user manu | Download Schneider Electric
FR: EM4300 series user manual -FR | Download Schneider Electric
Hope this helps,
Cesar
Link copied. Please paste this link to share this article on your social media post.
It does not help because on this page :
it's written :
type of measurement | Active and reactive power |
An not transmitting 3PH current, and 3PH Voltage
Posted: 2017-09-26 10:22 AM
Link copied. Please paste this link to share this article on your social media post.
Unfortunately, the EM4300 series only support maximum current and minimum voltage. 3-phase measurement support is only for energy, power and PF.