Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Search in
Link copied. Please paste this link to share this article on your social media post.
In the datasheet it is stated that Current per Phase is measured but the current measurement is not available in the COMX.
We have only maximum current over demand, which I guess is the maximum current recorded by the EM over all 15 minutes windows since start-up.
Same thing for Voltage measurement, only L1-N voltage is shown, no measurement regarding L2, L3 and only Minimum
Is-it normal ?
Kind regards
Posted: 2017-09-21 02:19 PM
Link copied. Please paste this link to share this article on your social media post.
Hi Guillaume,
Please refer to chapter 5 of the EM4300 series user manual for a list of measurements accessible through the Com'X series gateway:
EN: PowerLogic™ EM4300 series user manu | Download Schneider Electric
FR: EM4300 series user manual -FR | Download Schneider Electric
Hope this helps,
Cesar
Link copied. Please paste this link to share this article on your social media post.
It does not help because on this page :
it's written :
| type of measurement | Active and reactive power |
An not transmitting 3PH current, and 3PH Voltage
Posted: 2017-09-26 10:22 AM
Link copied. Please paste this link to share this article on your social media post.
Unfortunately, the EM4300 series only support maximum current and minimum voltage. 3-phase measurement support is only for energy, power and PF.

You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.