I have installed 5 ILM 62 motors in a machine. I changed one of the motor on new axis, But motor is running on the same old axis even at new location.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-09 12:45 AM
Hello @Asif1Mehmood
for the ILM motors, which type of IdentificationMode are you using? E.g. TopologyAddress or SercosAddress?
If you are using the TopologyAddress mode, when you exchange two motors, for example, they work exactly in the same way.
If you are using the SercosAddress mode, when you exchange two motors, the first one will behave like the second and viceversa. Probably you are in this situation.
I can help you further if you provide me a Diagnostics of your machine with a short description of the axis.
Some more info about the topology addressing you can find in this manual Lexium 62 ILM at page 67.
The Identificationmode parameter is shown in the picture below: