LXM28, Simple Speed Control Via Serial Modbus
Hi,
I am using LXM28 with a motor (BCH2). I would like to control the speed of the motor via Modbus, just do simple steps.
I have several issues for the setup:
1/ I can modify P3-06 and P4-07 with the keypad, but they are not permanent.
When I turned off and then turn on the drive, the settings go back to 0 for those parameters.
I used those parameters to be able to force the DI1-5: SON, TQL, SPD0, SPD1, Reset Fault.
Is there a way to make those settings (P3-06 and P4-07) can be saved in eeprom?
2/ With SoMove, I can see the right values of parameters P3.06 and P4.07 only if I turn the flag Exclusive ON.
Can I set the Exclusive flag on via Modbus? (Is the same as Access Lock register?)
3/ Using SOMove, I can't manage to rotate the motor. I thought by turning on SON bit I would start, the motor,
Is there a flag that needs to be turned ON?
SON is on.
SReady is ON
SPD0=1, SPD1=0
P1.09 = 1000
There is no error.
4/ What is the Modbus register to monitor the operating state?
Thank you for you support
Best,
KB
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-20 10:14 PM
For Modbus control of LXM26/28, activate permission first by P10-32(0xB40), then enable via P2-30=1(0x33C), reset fault with P0-01=0(0x102). For jog operations: P10-25(0xB32)=1(JOG+) or P10-25=2(JOG-); P4-05(0x50A)( JOG Velocity)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-01-20 10:14 PM
For Modbus control of LXM26/28, activate permission first by P10-32(0xB40), then enable via P2-30=1(0x33C), reset fault with P0-01=0(0x102). For jog operations: P10-25(0xB32)=1(JOG+) or P10-25=2(JOG-); P4-05(0x50A)( JOG Velocity)
Link copied. Please paste this link to share this article on your social media post.