Hi All,
I need o switch K1 and K2 in a TM3SAxx module but I only can with K1, do I need to have in account something special inside of the configuration?
Many thanks in advance,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-09 08:25 AM
Hello Pedro,
please refer to the hardware guide of the TM3 Safety Module and make sure you follow all safety instructions and information. You will find it on Schneider Electric website: TM3 Modules Hardware Guide
The behavior you described is correct according to the design of the TM3SA** module. To have K2 set "switched on" you must have Enable set TRUE in SoMachine.
A second condition is the terminals S41 – S42.
These can be used for EDM2 (External Device Monitoring) but have to be jumpered when not in use!
See picture below from instruction sheet:
Best regards
Ralf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-11-09 08:25 AM
Hello Pedro,
please refer to the hardware guide of the TM3 Safety Module and make sure you follow all safety instructions and information. You will find it on Schneider Electric website: TM3 Modules Hardware Guide
The behavior you described is correct according to the design of the TM3SA** module. To have K2 set "switched on" you must have Enable set TRUE in SoMachine.
A second condition is the terminals S41 – S42.
These can be used for EDM2 (External Device Monitoring) but have to be jumpered when not in use!
See picture below from instruction sheet:
Best regards
Ralf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of