How to scale analog input for M221?

Machine and Motion Control Forum

Support forum for Machine and Motion Control solutions, including Lexium MC12 and robotics, PacDrive, Modicon PLCs and I/Os, EcoStruxure Machine Expert Twin, … - from design, implementation to troubleshooting and more, by Schneider Electric

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Machine and Motion Control Forum
  • How to scale analog input for M221?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
9
FernandoRodrigues
FernandoRodrigues Support
7
LeTomas
Lt. Commander LeTomas Lt. Commander
5
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
Logic Controller - Modicon M221
product field
Schneider Electric
EcoStruxure™ Machine Expert - Basic

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Machine and Motion Control Forum
Start a Topic
Solved
jhonut
Ensign jhonut
Ensign

Posted: ‎2021-03-03 04:55 AM

0 Likes
9
15105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 04:55 AM

How to scale analog input for M221?

I have a TM221CE24R PLC with a TM3AI8 extension. I want to scale an extension's analog input signal . What function or how this could be done?

And another question would be how could I set for analog input channels: measurement type ( voltage, current (2 or 4 wire), resistor, etc), measurement range (0-10V, 0-20mA, 4-20mA, etc)?  

Labels
  • Labels:
  • Modicon M2xx
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic

Accepted Solutions
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-03-03 07:52 AM

In response to jhonut
1 Like
4
15089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 07:52 AM

You can static scale a Analog input directly via ESME Basic. You can see the needed fields in the attached screenshot.M2214.PNG

Minimum is the lowest value of the sensor at 0V

Maximum is the highest value of the sensor at 10V

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-03-03 08:15 AM

In response to jhonut
0 Likes
1
15072
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 08:15 AM

Hi you can add here a symbol name (IVALUE_1 as example) for the scaled value.

Or you can directly use the Hardware Address %IW1.0

TM221_6.PNG

In the example i use as scale 0...300 for a pressure probel 0..30Bar

In that case means the value 123 = 12,3 Bar.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-03-03 07:34 AM . Last Modified: ‎2021-03-03 07:34 AM

0 Likes
6
15095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 07:34 AM . Last Modified: ‎2021-03-03 07:34 AM

If you add in configuration the TM3 modul you can open via double click a menu were you canconfigure the Sensor Type and the scaling if you use a Voltage or a current input.

 

m2213.PNG

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jhonut
Ensign jhonut
Ensign

Posted: ‎2021-03-03 07:46 AM

In response to Bastian_Schmitz
0 Likes
5
15090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 07:46 AM

@Bastian_Schmitz, thanks for replying!

Any idea how to scale an analog input signal? I didn't find a function similar to the one existing in Machine Expert.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-03-03 07:52 AM

In response to jhonut
1 Like
4
15090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 07:52 AM

You can static scale a Analog input directly via ESME Basic. You can see the needed fields in the attached screenshot.M2214.PNG

Minimum is the lowest value of the sensor at 0V

Maximum is the highest value of the sensor at 10V

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jhonut
Ensign jhonut
Ensign

Posted: ‎2021-03-03 08:07 AM

In response to Bastian_Schmitz
0 Likes
2
15081
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 08:07 AM

@Bastian_Schmitz, I'm a little bit confused. I understood how scaling settings are being done. What I don't understand is how I assign the scaling result to a MW, MD or MF.

Let's say I have a temperature signal 4-20 mA. For 4mA I have 0 °C and for 20mA I have 65°C. These values, 0 and 65, where should be put? Where you wrote 4000 and 20000 for 4-20 mA? If, for example, I get 15mA, the scaling result is about 40°C. How do I get this result?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Ralf
Lieutenant JG Ralf Lieutenant JG
Lieutenant JG

Posted: ‎2021-03-03 08:09 AM . Last Modified: ‎2021-03-03 08:11 AM

In response to Bastian_Schmitz
0 Likes
0
15078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 08:09 AM . Last Modified: ‎2021-03-03 08:11 AM

Hi @Bastian_Schmitz,

thanks for your quick replies.

 

Hi @jhonut,

 

please find in addition the following link to a 25min video.

Analog input configuration is shown at around 7 min

https://www.youtube.com/watch?v=wE1owCFxO4I

 

Best regards 

Ralf

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2021-03-03 08:15 AM

In response to jhonut
0 Likes
1
15073
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 08:15 AM

Hi you can add here a symbol name (IVALUE_1 as example) for the scaled value.

Or you can directly use the Hardware Address %IW1.0

TM221_6.PNG

In the example i use as scale 0...300 for a pressure probel 0..30Bar

In that case means the value 123 = 12,3 Bar.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jhonut
Ensign jhonut
Ensign

Posted: ‎2021-03-03 11:27 PM

In response to Bastian_Schmitz
1 Like
0
15058
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-03 11:27 PM

I thought that symbol is assigned to analog input signal. Now it's clear. Thank you very much for your help!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Santito1-2023
Santito1-2023 Cadet
Cadet

Posted: ‎2023-08-24 02:57 AM

0 Likes
1
8384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-24 02:57 AM

I attach an example that uses a user function based on the equation of a straight line ( Y = mX+b )
Using the simulator you can see the behavior

 

Funcion de escalado.smbp

Reply

Link copied. Please paste this link to share this article on your social media post.

Santito1-2023
Santito1-2023 Cadet
Cadet

Posted: ‎2023-08-24 05:48 AM

In response to Santito1-2023
0 Likes
0
8375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-08-24 05:48 AM

fixed project (the above is an old undebugged version) : Funcion de escalado.smbp

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore