A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-04 03:24 PM
Hi,
I have enabled the 'WAITING' statement per below
I have been unable to use the statement due to syntax errors, see a test sample below.
I have also noticed that since I have enabled the 'WAITING' statement in the project options, I can no longer disable the WAITING statement as the check box is greyed out.
In other projects, I cannot enable the WAITING statement as the checkbox is greyed out too.
Interestingly, the editor dislikes bracketing inside the WAITING condition;
This is on EcoStruxure Machine Expert - HVAC v1.5.0 on Windows 10, Version 10.0.19045 Build 19045 for a target of TM172PDG18R bios 668.13.
What is going on? And how can I get WAITING working?
Cheers,
Jack
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-06 03:31 AM
Hi,
WAITING extension is supported only by target Secure Interface, this is why it's grey on other projects
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-06 04:51 PM
Hi @FedericoM
Ah ok, is there a bug with the greying out? It is not always greyed out when I am targeting a TM172PDG18R. If I connect to a simulation, the option becomes available, as soon as I disconnect, the option is greyed out again.
Cheers,
Jack