TM172 alarm detection

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • TM172 alarm detection
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
66
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
47
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Machine Expert - HVAC

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Solved
otrotabi
Lt. Commander otrotabi
Lt. Commander

Posted: ‎2022-11-07 05:10 AM

0 Likes
4
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 05:10 AM

TM172 alarm detection

I maybe missing something very obvious here.

 

Although in comparison a lot more limited than TM172, TM171 has a built in mechanism which allows to detect if anything is wrong as long as any item in the Alarms menu is set to 1. If that is so, then I can tell if an alarm is active by doing: 

 

AlarmActive := SysLocalLeds[16] = 1;

 

The Alarms menu does exist in TM172 as well. Is there any similar built-in mechanism ? I would like to avoid having to write a huge "OR" to detect an alarm.

 

Moreover, besides eventually using the Alarms folder to logically organize alarms (though Booleans seem to be easier to handle alarm visibility in the HMI), what is the functionality of this folder in TM172 ? I have not been able to find what it is useful for.

Labels
  • Labels:
  • HVAC
  • Tags:
  • ecostruxure
  • english
  • hvac
  • TM171
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
FedericoM
Commander FedericoM Commander
Commander

Posted: ‎2022-11-07 06:35 AM

0 Likes
1
872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 06:35 AM

Hello,

 

TM172 hasn't built-in functionalities related to alarms.

The solution is the one you mentioned, an OR among all managed alarms.

 

Folder alarm is present on TM172 just for portability reason of M171O projects.

 

On TM172, I suggest to define a Status variable for each alarm and show them on a dedicated folder of Commissioning/Installer and using the SET feature of the local/remote Display.

See Answer In Context

  • Tags:
  • english
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
FedericoM
Commander FedericoM Commander
Commander

Posted: ‎2022-11-07 06:35 AM

0 Likes
1
873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 06:35 AM

Hello,

 

TM172 hasn't built-in functionalities related to alarms.

The solution is the one you mentioned, an OR among all managed alarms.

 

Folder alarm is present on TM172 just for portability reason of M171O projects.

 

On TM172, I suggest to define a Status variable for each alarm and show them on a dedicated folder of Commissioning/Installer and using the SET feature of the local/remote Display.

  • Tags:
  • english
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

LeTomas
Lt. Commander LeTomas Lt. Commander
Lt. Commander

Posted: ‎2022-11-07 06:37 AM

0 Likes
1
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 06:37 AM

Hi @otrotabi ,

 

If I am not wrong i have asked to the experts the use of the "Alarms" on the "Configuration Tab" in ESME HVAC because I was not able to see the point for the M172 to use it because it does not create any variable on the display to use as alarm. I believe the answer was that the "Alarms" it is only for the M171O.

 

Best regards,

 

Leandro

Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
Lt. Commander otrotabi
Lt. Commander

Posted: ‎2022-11-07 07:05 AM

In response to FedericoM
0 Likes
0
867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 07:05 AM

Thanks for your answer.

 

Yes, I do use Sets to display the alarms. I have discovered that visibility of the distinct alarms maybe  set upon each alarm status (that is why the need to be boolean to make things easier)

 

However once I acknowledge them, I need a "global" alarm variable (this AlarmActive variable) to be able to display the alarm page again. Having to set the OR is another step you need not to forget. 

 

I wished all the alarm system could be made a little easier to manage. 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
Lt. Commander otrotabi
Lt. Commander

Posted: ‎2022-11-07 07:06 AM

In response to LeTomas
0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 07:06 AM

Thanks. Yes, indeed it does not seem to be of any use.

 

Regards

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of