M172 USB programing

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • M172 USB programing
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
66
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
47
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to HVAC and Pumping Forum
sardila
Ensign sardila
Ensign

Posted: ‎2022-11-07 02:53 PM

0 Likes
12
3012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 02:53 PM

M172 USB programing

Hi All,

I am currently facing a few strange behaviors when I am programming a M172 07-18I PLC using USB memory stick. After upgrading Ecostruxture to version 1.4 and the bios 668.12, I realized that the EEPROM variables are not being updated by the default values. It seems that now when programming using USB method will remain the EEPROM values set before the update.

In addition to this, when I tried to change value of variables on live debug mode, I could not change them and, I was seen wrong values on them (PLC Display/variables). Pictures attached
.

My question is, are there any bugs reported related? any way to make sure using USB programing method will wipe and set by default values on EEPROM variables? 

 

Before the Ecostruxture was updated the USB programming was setting back the default values on the variables.

 

Thanks in advance for the time.

 

Regards,

 

Attachments
Labels
  • Labels:
  • HVAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-11-07 10:36 PM

0 Likes
6
2998
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-07 10:36 PM

Yes in ESME HVAC 1.4 is a bug in the creating of the PARAM.BIN file for USB pendrive.

This issue will be fixed with ESME HVAC 1.5 

If you upload all Parameters manually you could load the correct PARAM.BIN file from the filesystem of TM172.

 

Your second problem looks like there is no communication between PLC and HMI part of the TM172PD.

Try to refresh the parameters in display part. If you rearrange the Modbus Register Addresses this could generate such a problem.

  • Tags:
  • english
  • ESME HVAC
  • TM172PDG18R
Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
Commander FedericoM Commander
Commander

Posted: ‎2022-11-08 03:06 AM

In response to Bastian_Schmitz
0 Likes
2
2993
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-08 03:06 AM

A patch for the PARAM.BIN creation is available at this link:

https://schneider-electric.box.com/s/svi3uam9raimwf51srhf70zv3idbup10

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sardila
Ensign sardila
Ensign

Posted: ‎2022-11-08 01:26 PM

In response to FedericoM
0 Likes
0
2989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-08 01:26 PM

Thanks Federico.

 

I received this patch from you on the 7th of July 2022 and it fixed the problem of generating the USB files, however, the issue now is related, but a bit different. I compared the files and it doesn't change anything from the version you share in July.

 

I have been working with this version 1.4 and I have programmed using USB files into more than 150 units. Some of the locations of the units are in remote areas. 

 

I am facing a serious problem because I am not 100% sure what are the implications of this bug. is it just affect the USB creation files? is this bug affect just the PLCs that were programmed before or also affect new PLCs (blank from Fabrique)?

 

I am curious why Schneider did not roll back version 1.4 due to the bugs found since Nov 2021 or before. I could not find any information related to the bugs reported on version 1.4. is there a list of known issues published anywhere that I can access?

 

Regards,

 

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sardila
Ensign sardila
Ensign

Posted: ‎2022-11-08 01:43 PM

In response to Bastian_Schmitz
0 Likes
2
2988
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-08 01:43 PM

Thanks Bastian,

 

I knew about the bug of creating USB files, but since I applied the suggested patch I have been programming more than 150 PLCs which probably will experience the same wrong operation. 

 

I think the second problem is a consequence of the USB files created using version 1.4, corrupted  PARAM.BIN could cause the storage of the wrong values on EEPROM variables. 

 

I would like to understand what are the reported bugs related to version 1.4 to take action on the way the production applications would be loaded into the PLC. 

 

Regards,

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-11-08 10:36 PM

In response to sardila
0 Likes
1
2971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-08 10:36 PM

The bug prevented the creating of the USB file PARAM.BIN which is needed to set the EEPROMs during project upload via USB pen drive. If you could crate the USB files without error the process should work.

 

Could you explain which differences between the value in ESME HVAC and your controler are still recognizable?

Please remind that the PARAM.BIN file use the values of the row  value and not of the row default.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

sardila
Ensign sardila
Ensign

Posted: ‎2022-11-13 02:09 PM

In response to Bastian_Schmitz
0 Likes
0
2943
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-13 02:09 PM

Hi Bastian,

The suggested patch was implemented and fixed the creation of USB files. However, when I deployed the application using the USB files, I found strange behaviour on the PLC. For instance, I have this simple instruction:

IF Room_Active <> EE_Room_Enabled THEN

sysVoid := sysWriteParBOOL(ADR(EE_Room_Enabled), Room_Active);

END_IF;

Every time the Room_Active Global variable changes the state the EEPROM variable is updated. When I program the PLC onsite, the variable EEPROM was TRUE after the update, and it didn’t change the value to false when I changed the Room_Active to FALSE.

This is just an example of the wrong behaviour I saw on the site. Values from Digital input/outputs and Boolean variables were totally wrong. String values on some variables were filled with wrong characters.

 

Regards,

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Adawas00
Adawas00
Cadet

Posted: ‎2024-06-18 04:39 AM

In response to FedericoM
0 Likes
0
1534
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-18 04:39 AM

Could I get the file link again? Because this one is no longer accessible.

Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
Commander FedericoM Commander
Commander

Posted: ‎2024-06-18 11:45 PM

0 Likes
1
1503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-18 11:45 PM

Hello,

the link is no longer needed, if you install Ecostruxure Machine Expert HVAC 1.6, the issue has been fixed

Reply

Link copied. Please paste this link to share this article on your social media post.

Adawas00
Adawas00
Cadet

Posted: ‎2024-06-19 12:19 AM

In response to FedericoM
0 Likes
0
1500
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-19 12:19 AM

Hi, 

I currently have version 1.6.0 installed and am experiencing a similar problem as before. In general, when uploading the program from a pendrive, the parameters set by default still do not upload. Maybe I am doing something incorrectly.

Previously having version 1.5.0 I used the patch and there was no problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2024-06-19 12:52 PM

0 Likes
0
1472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-19 12:52 PM

Did you update the target in your Project ESME HVAC? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Adawas00
Adawas00
Cadet

Posted: ‎2024-06-19 10:56 PM

0 Likes
0
1462
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-19 10:56 PM

Hello, 

I solved the problem by uploading the program in two parts.

First, I uploaded the full program generated by the ESME HVAC application, and then I uploaded only parameters (PARAM.BIN).

 

Thanks for your replies.

Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
Commander FedericoM Commander
Commander

Posted: ‎2024-06-20 11:02 PM

0 Likes
0
1447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-06-20 11:02 PM

This sounds strange...

Note that if you upload PLCIEC.COD and PARAM.BIN at boot the program and params are first uploaded and then executed.

If you do the same when the application is already running, you'll have to reboot the controller after the upload.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of