M172 PT100 Analog Input

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • M172 PT100 Analog Input
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
66
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
47
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Machine Expert - HVAC

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to HVAC and Pumping Forum
Khoa_NTM
Lieutenant | EcoXpert Master Khoa_NTM Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-09-16 10:05 PM

0 Likes
3
1057
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-16 10:05 PM

M172 PT100 Analog Input

Hello,

I want to connect PT 100, 3 wire to M172. Pls, help me configure AI and make an analog input register that can read from the Modbus pool. Many thanks

Khoa_NTM_0-1694927008794.png

 

Labels
  • Labels:
  • HVAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2023-09-17 10:50 PM

0 Likes
1
1037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-17 10:50 PM

Hi,

PT100 is not supported through M17x . 

The TM17x Series support only Temp probes with higher resistence values.

Like PT1000 NTC (20kOhm) or PTC.

I would suggest you use one of these Types.

If a PT100 is mandotory for you. Please check the Harmony Analog converters from Schneider Electric.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Khoa_NTM
Lieutenant | EcoXpert Master Khoa_NTM Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-09-21 10:03 AM

In response to Bastian_Schmitz
0 Likes
0
1006
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-21 10:03 AM

Hi,

I use the transmitter PT100 converter to output 4-20mA. (code: Seneca K120 RTD)

But the transmitter has no power supply. That means it must be connected to the PLC-type passive.

 

Please tell me how to connect the 4-20mA passive type to PLC M172. If yes, help me clear the blue area is a 4-20mA active type connection. The red area is a 4-20mA passive type, right?

Khoa_NTM_1-1695315806909.png

Thanks,

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2023-09-25 10:48 PM

1 Like
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-09-25 10:48 PM

Hi, yes use the red one to connect the converter 

Bastian_Schmitz_0-1695707326982.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of