Posted: 2023-09-17 10:50 PM
Hi,
PT100 is not supported through M17x .
The TM17x Series support only Temp probes with higher resistence values.
Like PT1000 NTC (20kOhm) or PTC.
I would suggest you use one of these Types.
If a PT100 is mandotory for you. Please check the Harmony Analog converters from Schneider Electric.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-21 10:03 AM
Hi,
I use the transmitter PT100 converter to output 4-20mA. (code: Seneca K120 RTD)
But the transmitter has no power supply. That means it must be connected to the PLC-type passive.
Please tell me how to connect the 4-20mA passive type to PLC M172. If yes, help me clear the blue area is a 4-20mA active type connection. The red area is a 4-20mA passive type, right?
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-09-25 10:48 PM
Hi, yes use the red one to connect the converter