Posted: 2024-10-09 04:32 AM . Last Modified: 2024-10-09 04:33 AM
I get this error while trying to add an EEPROM variable to a Menu
Cannot generate menu code (error message: Invalid Minimum value of parameter with IPA 47)
Since I could not figure out what was going on, I tried deleting it and creating a new variable. Now it generates basically the same error but it says:
Cannot generate menu code (error message: Invalid Minimum value of parameter with IPA8
Any idea what might be going on ?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-10 11:38 PM
Hi,
the error should be related to a minimum value not consinstent with the data type assigned to a Status variable or a EEprom parameter...you have probably deleted it.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-10 03:55 AM
Although the message is quite cryptic it seems to be related to either too many variables on the menu or too many EEPROM variables being used. I solved after deleting some variables I do not need for this project.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-10-10 11:38 PM
Hi,
the error should be related to a minimum value not consinstent with the data type assigned to a Status variable or a EEprom parameter...you have probably deleted it.