Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Support forum for Machine and Motion Control solutions, including Lexium MC12 and robotics, PacDrive, Modicon PLCs and I/Os, EcoStruxure Machine Expert Twin, … - from design, implementation to troubleshooting and more, by Schneider Electric
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-03 04:55 AM
I have a TM221CE24R PLC with a TM3AI8 extension. I want to scale an extension's analog input signal . What function or how this could be done?
And another question would be how could I set for analog input channels: measurement type ( voltage, current (2 or 4 wire), resistor, etc), measurement range (0-10V, 0-20mA, 4-20mA, etc)?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-03 07:52 AM
You can static scale a Analog input directly via ESME Basic. You can see the needed fields in the attached screenshot.
Minimum is the lowest value of the sensor at 0V
Maximum is the highest value of the sensor at 10V
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-03 08:15 AM
Hi you can add here a symbol name (IVALUE_1 as example) for the scaled value.
Or you can directly use the Hardware Address %IW1.0
In the example i use as scale 0...300 for a pressure probel 0..30Bar
In that case means the value 123 = 12,3 Bar.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-03 07:34 AM . Last Modified: 2021-03-03 07:34 AM
If you add in configuration the TM3 modul you can open via double click a menu were you canconfigure the Sensor Type and the scaling if you use a Voltage or a current input.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-03 07:46 AM
@Bastian_Schmitz, thanks for replying!
Any idea how to scale an analog input signal? I didn't find a function similar to the one existing in Machine Expert.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-03 07:52 AM
You can static scale a Analog input directly via ESME Basic. You can see the needed fields in the attached screenshot.
Minimum is the lowest value of the sensor at 0V
Maximum is the highest value of the sensor at 10V
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-03 08:07 AM
@Bastian_Schmitz, I'm a little bit confused. I understood how scaling settings are being done. What I don't understand is how I assign the scaling result to a MW, MD or MF.
Let's say I have a temperature signal 4-20 mA. For 4mA I have 0 °C and for 20mA I have 65°C. These values, 0 and 65, where should be put? Where you wrote 4000 and 20000 for 4-20 mA? If, for example, I get 15mA, the scaling result is about 40°C. How do I get this result?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-03 08:09 AM . Last Modified: 2021-03-03 08:11 AM
Hi @Bastian_Schmitz,
thanks for your quick replies.
Hi @jhonut,
please find in addition the following link to a 25min video.
Analog input configuration is shown at around 7 min
https://www.youtube.com/watch?v=wE1owCFxO4I
Best regards
Ralf
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-03 08:15 AM
Hi you can add here a symbol name (IVALUE_1 as example) for the scaled value.
Or you can directly use the Hardware Address %IW1.0
In the example i use as scale 0...300 for a pressure probel 0..30Bar
In that case means the value 123 = 12,3 Bar.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-03-03 11:27 PM
I thought that symbol is assigned to analog input signal. Now it's clear. Thank you very much for your help!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-08-24 02:57 AM
I attach an example that uses a user function based on the equation of a straight line ( Y = mX+b )
Using the simulator you can see the behavior
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-08-24 05:48 AM
fixed project (the above is an old undebugged version) : Funcion de escalado.smbp