Fast digital inputs TM172

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Fast digital inputs TM172
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
67
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
47
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Machine Expert - HVAC

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Solved
otrotabi
Lt. Commander otrotabi
Lt. Commander

Posted: ‎2022-11-15 03:32 AM

0 Likes
2
947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-15 03:32 AM

Fast digital inputs TM172

I need help regarding how to use TM172 fast digital inputs. As far as I know, digital inputs DI1 and DI2 in the whole line can either be used as regular digital inputs or as fast inputs.

 

I am sure this is documented somewhere, if so please let me know where to find the documentation.  I have checked all the documents I have and could not find it.

 

Following the convention followed on the published TDVAs I am naming inputs as per the following pic.

 

inputs.jpg

 

I then later reassign them to logical variables within a program called Physical_to_logical_inputs, the same concept used in TDVAs.

 

So, let´s say I add these new variables like in the picture and add these lines to Physical_to_logical_inputs program:

 

Status_udiCount1 := FI_Counter1;

Status_udiFreq1 := FI_Frequency1;

 

Is that all that it takes? In case I only need one fast input, for example DI1, is DI2 still available as a regular input?

 

What is the unit of FDI Frequency ? 

 

What do FDI*_value and FDI*_reset_counter mean  and how are they used ?

 

 

Labels
  • Labels:
  • HVAC
  • Tags:
  • ecostruxure
  • english
  • hvac
  • TM171
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
FedericoM
Commander FedericoM Commander
Commander

Posted: ‎2022-11-15 03:41 AM

0 Likes
1
944
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-15 03:41 AM

 

Hi,

 

here below the answers to your questions:

 

Is that all that it takes?

Yes, it is

 

In case I only need one fast input, for example DI1, is DI2 still available as a regular input?

Considering che common input, DI2 can be used as regular input

 

What is the unit of FDI Frequency ? 

[Hz/10]

 

What do FDI*_value and FDI*_reset_counter mean  and how are they used ?

FDI*_value is the current status of the input (like when you use it as regular input)

FDI*_reset_counter if set to true allows to reset the number of counted pulses

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
FedericoM
Commander FedericoM Commander
Commander

Posted: ‎2022-11-15 03:41 AM

0 Likes
1
945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-15 03:41 AM

 

Hi,

 

here below the answers to your questions:

 

Is that all that it takes?

Yes, it is

 

In case I only need one fast input, for example DI1, is DI2 still available as a regular input?

Considering che common input, DI2 can be used as regular input

 

What is the unit of FDI Frequency ? 

[Hz/10]

 

What do FDI*_value and FDI*_reset_counter mean  and how are they used ?

FDI*_value is the current status of the input (like when you use it as regular input)

FDI*_reset_counter if set to true allows to reset the number of counted pulses

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
Lt. Commander otrotabi
Lt. Commander

Posted: ‎2022-11-15 06:04 AM . Last Modified: ‎2022-11-15 06:28 AM

In response to FedericoM
0 Likes
0
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-11-15 06:04 AM . Last Modified: ‎2022-11-15 06:28 AM

😀

 

Pretty simple actually.  Thanks.

 

In the previous post you said :"The frequency is the one of the last period, so you might need to post filter it." Could you explain a little further ?

 

I noticed there´s a small lag between the time the signal in my scope goes to gnd and the time frequency reads 0 in the PLC. For this application it has no importance but I think that it eventually become important for other uses. Is that what you mean by post-filtering the signal? What kind of filters may be used ?

 

As a side note: is a pull up resistor advised  ?

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of