BSH Motor Holding Brake Failures

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • BSH Motor Holding Brake Failures
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
66
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
47
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to HVAC and Pumping Forum
VaughnKretzmann
Ensign VaughnKretzmann
Ensign

Posted: ‎2021-08-22 11:59 PM

1 Like
1
1172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-22 11:59 PM

BSH Motor Holding Brake Failures

We were called to a machine with the following Servo equipment:

3 X LXM05AD57N4

3 X BSH1402P11F2A

Controlled by a TSX37 PLC via CAN.

 

The customer has lost 8 servomotors on this machine in a short space of time.  All the failures were the mechanical holding brake coil that had failed/burnt.  The resistance is lower than the typical 23ohms and then the brake does not disengage when power is applied to the brake.   

 

The next item to fail is the Servo Motor Power cable.   The pin on one of the motor phases is found to be shorter and it is black inside the connector indicating arcing from the pin that has "melted" due to excessive motor current possibly because the brake is not disengaging.

 

We will investigate the parameters in the LXM05 if they are correct to protect the motor and cable from overcurrent but what we have found is that the OEM did not use a HBC holding brake controller and the brake is controlled from the TSX37 PLC via a mechanical relay.   

 

We are going to do a more thorough investigation when we return to site but our question is: 

Would the failure of the brakes be due to the fact that there is no voltage reduction?   

 

The HBC controller has the facility to reduce the holding brake voltage after 1s to reduce the power and heat  but in the LXM05 manual it indicates that this should be switched on for SER motors but not for BSH motors.   The LXM32 has the HBC controller built into the Servo Drive and does not seem to have the option to switch off the voltage reduction.

 

Could someone confirm whether the voltage reduction is definitely required for the BSH motors and if we are correct in thinking that this is the probable cause of the mechanical brakes failing?

Labels
  • Labels:
  • Lexium
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
VaughnKretzmann
Ensign VaughnKretzmann
Ensign

Posted: ‎2021-08-24 05:50 AM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-24 05:50 AM

@Vikash_Rampathi please can you try elevate this issue to someone who can assist as the client needs a solution as soon as possible.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of