Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-04 08:04 PM
I created notification class in Machine Expert HVAC. But I cannot find where I can create BACnet Alarm to use the class. So I discovered the M172 in workstation and tried to create in workstation. However, warming " object dynamic creation not supported".
My question are:
1) How can I use the notification class (I know this class is used for BACnet Alarm)
2) How can I create object in workstation
3) If I can create the object in workstation, will I also observe these object in Machine Expert - HVAC?
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-05-04 11:09 PM
Updated: Now , I already know how to apply the notification to each point. However, the alarm state is always shown "normal" but the event state show normally (High limit or Low Limit as what I expected) , How can I change to apply the notification?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-08-21 03:13 AM . Last Modified: 2021-08-21 03:15 AM
Hello @summersiu
Can you write value from EBO to Status Variable or EPPROM using BACNET/IP?
I'm just got the value (on Eco HVAC) but can not write to Status variable
Can you help me?