Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

BRX PLC connecting to a ATV630 via Modbus TCP

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • BRX PLC connecting to a ATV630 via Modbus TCP
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Captain FedericoM Captain
93
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
56
M_Cervati
M_Cervati Support
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to HVAC and Pumping Forum
Start a Topic
meridianelect
Crewman meridianelect
Crewman

Posted: ‎2022-05-19 01:45 PM

1 Like
5
2698
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-19 01:45 PM

BRX PLC connecting to a ATV630 via Modbus TCP

Having trouble reading Modbus address 403202 (motor frequency ).I have tried other addresses but all I get a reception code 2 .the only one I have managed to get to work is 400001 without a error and that is not even a valid address .

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-05-20 05:22 AM

0 Likes
3
2678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-20 05:22 AM

Which Unit ID did you use? If you use 255 you talk only to the IO Scanner which are defined in the VSD. If you want to read random parameter you need to use a differen Unit Id between 1...247 which is definded as Modbus RTU Address in the VSD. (don´t forget to resart the VSD after configuration of the Modbus RTU address)

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

meridianelect
Crewman meridianelect
Crewman

Posted: ‎2022-05-20 06:45 AM

In response to Bastian_Schmitz
0 Likes
2
2665
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-20 06:45 AM

I was using unit ID 255 ,as that is the default and recommended setting in the BRX.IF I change it to unit 0 (I have another Brand ,a CLICK PLC working just great on unit #0)than It still gives me a error but exception code is now 1.what causes this code ?any ideas?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

LeTomas
Lt. Commander LeTomas Lt. Commander
Lt. Commander

Posted: ‎2022-05-20 06:55 AM

0 Likes
0
2662
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-20 06:55 AM

HI @meridianelect ,

 

The ATV6xx has a "Drive I/O Profile" table where you can configure which information you can read/write from/to the drive.

 

Image_Drive.PNG

 

In order to access to that information you will need to look at the address 0 (check in your system if you need to add 1 or not), take a look in the configuration in one of our software with the ATv6xx via ModbusTcp IOscanner:

 

IMage_ESME.PNG

I hope this can help you.

 

Best regards,

 

LeTomas

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2022-05-22 10:59 PM

In response to meridianelect
0 Likes
1
2612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-22 10:59 PM

If you use Unit Id 0 you will send a broadcast message were you donot get an respones. This could be the reason why you get shown a error. If you wan´t directly read/write the parameters you need to activate a modbus RTU address and use the dedicated Unit id. Or you need to configure the IO Scanner like from LeTomas described.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

meridianelect
Crewman meridianelect
Crewman

Posted: ‎2022-05-23 06:57 AM

In response to Bastian_Schmitz
0 Likes
0
2597
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-23 06:57 AM

I have it working now ,The unit ID was the Issue .IN somove software under the "MY Device" tab in the structure box it will tell you Info on the Modbus Slave. the Id you use is 248 .All my Schneider drives have that as there Id number ,not sure if that changes on newer models but it worked for my application .

 

 

 

 

 

 

Screenshot 2022-05-23 075033 so move.png

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore