Machine Automation Forum
A forum addressing machine automation solutions for the complete machine lifecycle. Including offers like Machine Advisor, Modicon PLC/PacDrive, Lexium or Preventa. Discuss and share knowledge on offers relating to cloud-based service platforms, machine localization and monitoring, industrial operations control, motion products as well as safety function!
Link copied. Please paste this link to share this article on your social media post.
Posted: 4 weeks ago
Hi,
I want to set up the STO function on the ATV320 inverter. I need to use the External device monitoring to achieve Cat4 safety requirement. There doesn't seem to be a dedicated EDM output, can the DQ+, DQ- be used as EDM feedback?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 3 weeks ago
Hi,
We can configure the output DQ as feedback from the STO. A screenshot of SoMove and the Safety functions manual, which contains wiring diagrams according to Safety CAT, are attached
.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 3 weeks ago
Hi, thanks for the feedback it was very helpful. I didn't initally see the feedback options for the DQ assignement. I see the "power removal state" is the correct selection.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.