Issue
"Completion event failure" and/or "Waiting for unit to restart" errors are received when attempting to download a controller which has already been commissioned and contains an existing Menta application.
Product Line
TAC Vista
Environment
- LNS Network
- Xenta Programmable controllers
- Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B
- System Plug-in
Cause
The controller is busy responding to all other requests for communication and is not able to focus solely on the download.
Resolution
- Before downloading, right-click on the controller and select Manage
- Set the node status to offline
- Download the controller
- Set the node status back to online.
Alternatively,
- Before downloading, de-commission the unit. Select “Preserve neuron ID" to allow the plug-in to communicate with the controller and to avoid having to re-enter the ID or service pin.
- Download the controller
- Re-commission the device. This will prevent the controller from performing other communication while trying to receive the download and thus being unable to keep up.