WorkPlace Tech 5.8.x, 5.9.x, 5.10.x, and 5.11.x Operating System and Microsoft Visio Compatibility

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • WorkPlace Tech 5.8.x, 5.9.x, 5.10.x, and 5.11.x Operating System and Microsoft Visio Compatibility
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
17429 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

WorkPlace Tech 5.8.x, 5.9.x, 5.10.x, and 5.11.x Operating System and Microsoft Visio Compatibility

Picard Product_Support
‎2020-12-15 10:46 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Issue

WorkPlace Tech 5.8.x, 5.9.x, 5.10.x, and 5.11.x Operating System and Microsoft Visio Compatibility

Product Line

TAC IA Series

Environment

  • WorkPlace Tech Tool Software release 5.8.x, 5.9.x, 5.10x, and 5.11.x
  • Microsoft Windows and Microsoft Office Visio requirements, see the "Resolution" section, below.
  • Visio 2010, 2013, 2016, 2019, 2021(.msi install) 
  • Visio 2013, 2016, 2019, 2021 (subscription "Click to Run", Plan 2)
  • Office 2010, 2013, 2016 (.msi install)
  • Office 2013, 2016, 365 (subscription "Click to Run", Plan 2)
  • Support for Workplace Tech 5.10 / previous and Workplace Tech Editor
  • Note: Visio 2019 and Visio 2021 are not supported in 5.9.4 or EBO versions before EBO 2022.  Visio 2019 and Visio 2021 are supported when using Workplace Tech 5.10.x and EBO 2022.

Cause

What Microsoft Windows operating systems and what versions of Microsoft Visio are compatible with the WorkPlace Tech Tool version 5.8.x, 5.9.x, 5.10.x, and 5.11.x?

Resolution

Microsoft Windows

WorkPlace Tech Tool releases 5.8 through 5.8.6 are certified to run on the following versions of Microsoft Windows:

  • Microsoft Windows XP Professional with Service Pack 2 or Service Pack 3
  • Microsoft Windows Vista 32-bit Business, Ultimate or Enterprise
  • Microsoft Windows 7 32-bit Professional
  • Microsoft Windows 7 64-bit Professional

WorkPlace Tech Tool release 5.8.7 is certified to run on the following versions of Microsoft Windows:

  • Microsoft Windows 7 32-bit Professional
  • Microsoft Windows 7 64-bit Professional
  • Microsoft Windows 8.1 32-bit Pro or Enterprise
  • Microsoft Windows 8.1 64-bit Pro or Enterprise
  • Microsoft Windows Server 2012 64-bit

WorkPlace Tech Tool releases 5.9.1 to 5.9.4 are certified to run on the following versions of Microsoft Windows:

  • Microsoft Windows 7   32-bit Professional
  • Microsoft Windows 7   64-bit Professional
  • Microsoft Windows 8.1   32-bit Pro or Enterprise
  • Microsoft Windows 8.1   64-bit Pro or Enterprise
  • Microsoft Windows 10    32-bit Professional
  • Microsoft Windows 10    64-bit Professional
  • Microsoft Windows Server 2012   64-bit

WorkPlace Tech Tool release 5.10.0 to 5.10.x is certified to run on the same as WorkPlace Tech 5.9.x and the following versions of Microsoft Windows:

  • Microsoft Windows Server 2016 64-bit
  • Microsoft Windows Server 2019 64-bit
  • Microsoft Windows Server 2022 64-bit
  • Microsoft Windows 11 Professional (Workplace Tech 5.10.4 only)

WorkPlace Tech Tool release 5.11.0 is certified to run on the following versions of Microsoft Windows:

  • Microsoft Windows 10 64-bit Professional
  • Microsoft Windows Server 2022 64-bit
  • Microsoft Windows 11 Professional

Microsoft Visio

Microsoft Windows 7 32-bit Professional
Microsoft Windows 7 64-bit Professional
Microsoft Windows 8 32-bit Pro or Enterprise
Microsoft Windows 8 64-bit Pro or Enterprise
Microsoft Windows 8.1 32-bit Pro or Enterprise
Microsoft Windows 8.1 64-bit Pro or Enterprise
Microsoft Windows Server 2012 64-bit

WorkPlace Tech Tool releases 5.8 through 5.8.6 require one of the following versions of Microsoft Visio (32-bit version ONLY)

  • Microsoft Office Visio 2003 with Service Pack 3 (officially supported for WPT 5.8.0, WPT 5.8.1, no known issues with WPT 5.8.2 through 5.8.5)
  • Microsoft Office Visio 2007 with Service Pack 1 or Service Pack 2
  • Microsoft Office Visio 2010 with or without Service Pack 1
    NOTE: Standard or Professional edition of Microsoft Visio may be used.

WorkPlace Tech Tool release 5.8.7 requires one of the following versions of Microsoft Visio (32-bit version ONLY)

  • Microsoft Office Visio 2007 with Service Pack 3
  • Microsoft Office Visio 2010 with Service Pack 2
    NOTE: Standard or Professional edition of Microsoft Visio may be used.

WorkPlace Tech Tool release 5.9.1 through 5.9.4 requires one of the following versions of Microsoft Visio (32-bit version ONLY)

  • Microsoft Office Visio 2010 with Service Pack 2
  • Microsoft Office Visio 2013 with Service Pack 1
  • Microsoft Office Visio 2016
    NOTE: Standard or Professional edition of Microsoft Visio may be used.

WorkPlace Tech Tool releases 5.10.0 through 5.10.x requires one of the following versions of Microsoft Visio (32-bit version ONLY)

  • Microsoft Office Visio 2016
  • Microsoft Office Visio 2019
  • Microsoft Office Visio 2021
  • Microsoft Office Visio Office 365 Subscription Plans 2

WorkPlace Tech Tool releases 5.11.x requires one of the following versions of Microsoft Visio (64-bit version ONLY)

  • Microsoft Office Visio 2019 64-bit
  • Microsoft Office Visio 2021 64-bit
  • Microsoft Office Visio Office 365 Subscription 64-bit Plans 2

Warning: WorkPlace Tech 5.11 is not compatible with EBO WorkPlace Tech Editor. Do not install WP Tech 5.11 on a PC that has EBO WorkPlace Tech Editor installed. Continue to use WP Tech 5.10 on PCs where EBO WorkPlace Tech Editor is required.

 

Note: Workplace Tech Tool 5.10.0 and later releases require .NET Framework 4.8 to support Open LDV 5.1 which is included in the installer.  .NET Framework 3.5 Sp1 is no longer required.

 

Follow the instructions in the article link for the security updates required. Workplace Tech 5.10.x and previous / Workplace Tech Editor (EBO) Microsoft Security Updates required...

For the Visio requirements for earlier versions of the WorkPlace Tech Tool software, see What versions of Visio are required for WorkPlace Tech?.

Labels (1)
Labels:
  • TAC IA Series
Tags (8)
  • Find more articles tagged with:
  • 6025
  • office
  • RandyDavis20
  • RandyDavis22
  • RandyDavis23
  • RandyDavis24
  • visio
  • workplace tech
Was this article helpful? Yes No
100% helpful (8/8)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore