Issue
When accessing the Xenta 555 web interface, certain pages—such as the Time Schedule—may appear grayed out or inaccessible.
Product Line
Satchwell MicroNetEnvironment
- Xenta 555 Controller
- Xbuilder Software
Cause
This issue typically occurs due to a mismatch between the Xenta 555 firmware version and the Xbuilder software version used to create or edit the project.
Resolution
To resolve this issue, ensure that the Xbuilder version matches the firmware version of your Xenta 555 device. Below is a compatibility matrix:
| Xenta Firmware Version | Required Xbuilder Version |
|---|---|
| 5.00 | 5.00 |
| 5.01 | 5.01 |
| 5.02 | 5.02 |
| 5.03 | 5.03 |
| 5.10 | 5.10 |
| 5.11 | 5.11 |
| 5.12 | 5.12 |
| 5.13 | 5.13 |
Example:
If your Xenta 555 is running firmware version 5.1.1, and your project was created in Xbuilder 5.0.3, follow these steps:
- Install Xbuilder 5.1.1.
- Open your project in Xbuilder 5.1.1.
- The project will be automatically upgraded.
- Upload the upgraded project to the Xenta 555.