What does the "| n" mean when viewing the properties of an OPC variable in Vista workstation?
  • What does the "| n" mean when viewing the properties of an OPC variable in Vista workstation?
  • sesa177673
    sesa177673
‎2018-09-06 03:31 PM
  • Problems have been encountered with OPC variables
  • Error messages such as "The object is no longer available in the servers address space",
  • Also, canonical data type or OPC data types.
Vista 5.1.X
TAC Vista OPC client
The "|n" is a reference to the data type or canonical data type as it's called in the OPC standard. In the world of OPC, the client application can be created in on one of many diverse programming languages. To resolve potential issues all OPC data types are assigned a specific Canonical Data Type. When a client application adds an OPC Item to an OPC Group it can use the default data type for the item or it can request the item with a specific canonical data type. If the OPC tool is used then the canonical is added automatically by checking with the server. It's only if variables are added manually that this information is required.
The method used for addressing OPC variables is Folder.Variable_Name|Data_Type
 The table below details the data types:
Data Type
Canonical Type
Size
Data Range
Boolean
11
1 Bit
True or False
Byte
17
1 Byte
0-255
Byte Array∗
8209
1 Byte times Array Size
0-255
Short
2
2 bytes
-32768 – 32767
Short Array∗
8194
2 bytes times Array Size
-32768 – 32767
BCD
18+
2 bytes
0 - 9999
BCD Array∗
8210
0 - 9999
Word
18
2 bytes
0 – 65535
Word Array∗
8210
0 – 65535
Long
3
4 bytes
-2,147,483,648 to 2,147,483,647
Long Array∗
8195
4 bytes times Array Size
LBCD
19+
4 bytes
0 - 99999999
LBCD Array∗
8211
0 - 99999999
Dword
19
4 bytes
0 – 4,294,967,295
Dword Array∗
8211
0 – 4,294,967,295
Float
4
4 bytes
-(3.40 E38 – 1.40 E-45) to (1.40 E-45 – 3.40 E38)
Float Array∗
8196
Double
5
8 bytes
-(1.798 E308 – 4.941 E-324) to 4.941 E-324 – 1.798 E308)
Double Array∗
8197
8 bytes times Array Size
Char
16
1 Byte
All Characters supported in the standard ASCII table
String
8
1 – n Bytes
  • 7581
This is a heading