What cable type should be used for BACnet MS/TP communications?
  • What cable type should be used for BACnet MS/TP communications?
‎2018-09-07 02:08 PM
Last Updated: Crewman ContentModerator ‎2025-10-15 03:41 AM
What specification should BACnet MS/TP cable meet?
Andover Continuum, EcoStruxure Building Operation
MS/TP BACnet devices
Often an incorrect cable type is used when wiring MS/TP devices causing unreliable communications.
The BACnet Controller Technical Reference defines the following cable specification for a MS/TP cable:
RS-485 Cable Specifications:
  • Cables used to form the RS-485 network should conform to the following specifications:
  • Wire Size: 22-24 AWG
  • Cable Type: Twisted-pair, copper wire, tinned
  • Shield: Braid
  • Nominal Impedance: 100-120 Ohms
  • Velocity of propagation: 78%
  • Capacitance: <12.5 pF/ft (~ 41pF/M) between conductors and < 22 pF/ft (~72pF/M) between the conductor connected to ground and the next conductor.
An example of a cable that meets this specification is Belden 3105A.
Also check out the SmartStruxure-RS485-Network Installation Quick-Help video on the Exchange.
Labels (2)
Tags (2)
  • 4889
  • ChrisAsbury22
100% helpful (4/4)