Weather information provided through the weather module in I/A Series G3 is no longer updating

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Weather information provided through the weather module in I/A Series G3 is no longer updating
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2994 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Weather information provided through the weather module in I/A Series G3 is no longer updating

Picard Product_Support
‎2018-09-11 01:22 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:23 AM

Issue

Weather information provided through the weather module in I/A Series G3 is no longer updating.

Product Line

TAC IA Series

Environment

  • I/A Series G3 Enterprise Network Server
  • ENC-410
  • ENC-520

Cause

The National Weather Service hosts the data service used by the Niagara weather module's default provider, the "NWS Weather Provider".

At some point during the week of September 26th, the National Weather Service moved the location of their forecasted weather conditions service.  No advanced warning of the change was provided.

The error message encountered may include:

WARNING [10:04:20 30-Sep-11 EDT][weather] Updating forecast failed for WeatherReport
javax.baja.sys.BajaException: 404 Not Found
at com.tridium.weather.nws.NwsForecastReader.getFeed(NwsForecastReader.java)
at com.tridium.weather.nws.NwsForecastReader.getFeed(NwsForecastReader.java)
at com.tridium.weather.nws.NwsForecastReader.getFeed(NwsForecastReader.java)
at com.tridium.weather.nws.NwsForecastReader.getForecast(NwsForecastReader.java)
at com.tridium.weather.nws.BNwsWeatherProvider.updateReport(BNwsWeatherProvider.java)
at javax.baja.weather.BWeatherReport.doUpdateWeatherReport(BWeatherReport.java)
at auto.javax_baja_weather_BWeatherReport.invoke(AutoGenerated)
at com.tridium.sys.schema.ComponentSlotMap.invoke(ComponentSlotMap.java)
at com.tridium.sys.engine.EngineUtil.doInvoke(EngineUtil.java)
at javax.baja.sys.BComponent.doInvoke(BComponent.java)
at javax.baja.util.Invocation.run(Invocation.java)
at javax.baja.util.Worker.process(Worker.java)
at javax.baja.util.Worker$Processor.run(Worker.java)
at java.lang.Thread.run(Thread.java:823)

Resolution

The weather service has been updated in patched weather modules to use the new data service location.  A number of other enhancements have also been made to better detect this situation and attempt to automatically resolve the issue by better following the 'HTTP Moved Permanently' error response messages. This may help reduce the impact of future unannounced National Weather Service data service changes.

Although some users may wish to work around this problem by making changes to hidden fields on the weather provider, this is not recommended because it leaves stations exposed problems resulting from future data feed changes.

forecast server: graphical.weather.gov
forecast path: /xml/sample_products/browser_interface/ndfdBrowserClientByDay.php

The NWS has also deprecated the current condition feeds previous retrieved from the www.nws.noaa.gov servers. These are now being replaced by feeds made available at www.weather.gov.  The new patched weather module will automatically use the feeds at the new location. As a temporary workaround, the Nws Weather Provider's hidden slot "conditions server" can be modified with the new value "www.weather.gov".

It is recommended that weather service users upgrade to the most recent weather module for their release.  The modules can be downloaded from The Exchange Download Center.

weather-3.4.67.3 or higher
weather-3.5.39.5 or higher
weather-3.6.37.4 or higher

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6233
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore