Using AIC to trigger an event sequence
  • Using AIC to trigger an event sequence
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-06 01:16 PM
Using Access Initiated Control to trigger an event sequence
I/NET Seven
7798
Custom door applications sometimes require several steps to be initiated on a reader entry
  1. Create in Internal DO point (Point1) where 0 = off and 1 = ON, The scan interval should be shorted than the expected time between 2 card reads at the door.
  2. Add a Calculation to point1 that sets it equal to 0. [C0 where C0=0]
  3. Add an event extension to the point that triggers your desired event sequence on the specified state of ON
  4. Create an AIC that starts point1 on a reader Entry
  5. Create your event sequence with the desired programming.
The effect should be that a reader entry causes Point1 to turn on triggering the event sequence
  • TAC INET
  • 6229